In the 2015 International Building Code, Section 101.2:
The provisions of this code shall apply to the construction, alteration... of every building or structure in any appurtenances connected or attached to such buildings or structures. Exception: Detached one- and two-family dwellings and multiple single-family dwellings (townhouses) not more than three stories above grade plane in height with a separate means of egress, and their accessory structures not more than three stories above grade plane in height, shall comply with the International Residential Code. The debate: Why in the world are we going to allow them to label this design as residential? The townhouse exception is seemingly being used pretty loosely around the building department. In our college community, these structures meet the requirements of a townhouse, but with obvious intent to be student housing. After looking at code....I cant say I blame these designers. I see no way to combat their argument. They meet all the code requirements to avoid the extra costs of a 13R system and only have to add an additional layer of gyp to comply!? If I am missing something, please let me know! Maybe I just need to accept them as townhouse? It sure doesn't "feel" right. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
23 Comments
Pete H
12/28/2022 06:50:22 am
The student dwellings have separate paths of egress from each individual unit? They don't have to go to a common hallway for egress?
Reply
Aaron Easter
12/28/2022 12:16:50 pm
Yes, all of these townhouses are getting 13D systems. I guess I am just wondering why the one down the street is an R2 and installing a 13R system.
Reply
Aaron Easter
12/28/2022 01:52:55 pm
....ans yes, it meets all the ICC requirments for Townhouse and is NOT on campus or owned by the campus. The intent of the structure is 100% for student use.
Reply
Todd E Wyatt
12/28/2022 08:16:25 am
This "exception" simply points us to the International Residential Code (IRC) for Code compliance ... it does not eleviate the Code requirements for this building type IF it meets all of the requirements (e.g. 3 stories or less above grade plane, separate Means of Egress) and it meets the definition of "townhouse" (A single-family dwelling unit constructed in a group of three or more attached units in which each unit extends from the foundation to roof and with open space on at least two sides.) and "dwelling unit" (A single unit providing complete, independent living facilities for one or more persons, including permanent provisions for living, sleeping, eating, cooking and sanitation).
Reply
Aaron Easter
12/28/2022 12:24:59 pm
Correct. It seems like there are systems ran off domestic water pressure (13D) that really should have the R2 label. When I imagine a townhouse, I see attached structures (3 or more) that are able to be sold individually. The code does not require that! All of these dwellings can be on the same lot. In all fairness, I do view a duplex as residential. 3 story buildings with each dwelling being 3 stories high just “seems” to be in a different category. By code, I it isn’t. Maybe the answer is just to accept it.
Reply
Darin Golden
12/29/2022 08:53:36 am
The answer for an AHJ is to always accept the adopted regulations whether you agree with them or not. Don’t fall into the trap of what you think it should say or should require. Code is developed through a consensus process that is highly debated and yes, at times politicized. If you think it should say something different, get on a committee and convince your peers and/or submit proposals.
Jay
12/28/2022 08:46:49 am
I would look at the use rather than only the construction features. Like when a structure was originally constructed and occupied as a single family home (governed by IRC) but has now been rezoned and is used as a dentist office or mercantile, which causes the structure to be governed by the IBC, even though it still looks like a one-family dwelling. Unfortunately the IRC doesn't define single family or even one-family dwelling. But I would refer to the definition of dormitory in IBC "....for persons not members of same family..."
Reply
Aaron Easter
12/28/2022 12:31:14 pm
I agree with you here….BUT. This means I as a reviewer would be researching and questioning things that are outside of my scope:
Reply
Paul Pinigis
12/28/2022 09:13:03 am
Townhouses are exempt from the IBC simply because they fall under the purview of the IRC. You argue that this is student housing, but Is student housing somehow not residential? If these dwellings are built as townhouses, and used for residential purposes, how is conformance with the IRC less than adequate in your view?
Reply
Aaron Easter
12/28/2022 12:40:48 pm
That is the same thing the Building Official has said in our conversations.
Reply
Darin Golden
12/29/2022 08:48:34 am
1. There’s not much difference between a 13D and 13R system when installed in Group R3 Townhomes and Group R2 Apartments/Condos. Both have similar size compartments so the up to 4 head calc in a 13R usually maxes at a 1-2head calc on the second or third floor making it the same as what a 13D would be called at. Also, both standard allow a combination feed so their isn’t much, if any cost difference in these types of structures.
sean
12/31/2022 08:41:51 pm
single family is not an occupancy type.
Aaron Easter
1/4/2023 08:24:05 am
Thanks for the info Darin. That gives me some peace of mind. It just seems odd that on campus it’s an R2 no matter, but across the street off campus, builder can decide. It does meet code though!
Jesse
12/28/2022 10:09:37 am
I'm afraid I don't see the issue here. Would it not be residential??
Reply
Aaron Easter
12/28/2022 12:42:30 pm
It is but there are things they avoid in taking the townhouse exception.
Reply
Will Warlick
12/28/2022 10:29:20 am
Dormitories built under the IRC seems wrong. The code recognizes a higher hazard specific to dormitories. See 2018 IBC 420.10 (dormitory cooking facilities) for example. The code assigns a specific occupancy group classifications to dormitories: R-2 or R-3. It also defines dormitories, and provides other specific requirements for this use (see 2018 IBC 806.2 and Table 1004.5, and IFC 308.4.1, 403.10.2.3, 805.4, 807.2, 807.5.6, 808.2, 904.13 and 906.1, and IPC Table 403.1).
Reply
Aaron Easter
12/28/2022 12:50:34 pm
This is EXACTLY what I am trying to convey to my building official. These are all private investors and they will almost surely rent by room not unit.
Reply
Chad
12/28/2022 01:35:56 pm
That not a life safety issue... on paper. We cannot out regulate greed in the name of safety because the politicians will not allow it.
sean
12/31/2022 08:38:45 pm
how they rent them has no bearing on the code.
Aaron Easter
1/4/2023 08:18:57 am
That is a bit of my issue. The college would be required to label these R2, but off campus used in the exact manner gets the townhouse exemption. I was happy to read Darin Holden’s response to another thread above. 13D and 13R capabilities are similar.
Patrick Drumm
1/26/2023 10:02:33 am
I don't think it is overreacting because these allowances can have implications down the line. Imagine if you lived in Rhode Island. The Building Code allows these townhomes to be treated as Residential. The section below eliminates the requirement for sprinklers in the residential code, but gives the owner the option. Not many owners opt to spend that money...
Robert Hughes
12/28/2022 02:03:36 pm
Safety is no longer first.
Reply
Joshua Perez
8/30/2023 12:51:18 pm
If this is a sprinkler issue - let's remember there are plenty of jurisdictions that have stripped the requirement of an automatic suppression system from their adopted version of the IRC. Kentucky for example, does not require suppression in single or two family residential occupancies.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop June '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
July 2024
PE PREP SERIES |