I have a standpipe demand of 750gpm. I am providing a fire pump for the system demand.
Should I be selecting a 750 gpm pump or a 1000 gpm pump, based on adding a safety factor (or other reasoning)? My sprinkler demand is less than 750 gpm so I would only need to provide the 750 gpm for the standpipes. Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
10 Comments
Pete H
8/22/2023 07:22:27 am
750 is probably fine.
Reply
Anthony
8/22/2023 07:29:55 am
Assuming you only have 2 standpipes, 750 will be fine. Run a calc. Standpipe calc's can be done in excel. Select a pump with enough pressure to overcome the friction loss. You shouldn't have overflow problems with 3 flowing hose valves.
Reply
Dan Wilder
8/22/2023 08:03:12 am
At 750 GPM (assuming this is required to be an automatic standpipe), no issue at all as that covers both your sprinkler and standpipe demands, just watch out for overpressure issues on the lower floors. 13'-22 19.1.6.3.1 allows omission of inside hose allowances with a combined sprinkler/standpipe within fully sprinklered building and a Class I or III standpipe so even with a sprinkler demand close to 750 or slightly over, the water supply becomes the mitigating factor, not the pump rating.
Reply
Glenn Berger
8/22/2023 08:10:47 am
Based on what have described a 750 gpm fire pump would be acceptable.
Reply
Eric R
8/22/2023 08:18:14 am
NFPA-20 allows a centrifugal fire pump to supply a system up to 150% of its rated flow, with the annex adding in that the recommended range is 90%-140% of rated flow.
Reply
Jesse
8/22/2023 09:47:11 am
I'm presuming you're calculating 2 standpipes for a demand of 750-gpm. A 750-gpm pump should work just fine.
Reply
Alex
8/22/2023 11:58:37 am
Run a calc and see where you land on your curve. I would say a 750 GPM is fine from what you said.
Reply
Chris
8/22/2023 12:23:21 pm
Perhaps a dumb question, but do you need a pump? can you get away with a manual standpipe?
Reply
Ed
8/22/2023 09:16:17 pm
My thoughts are the question shouldn’t be whether
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop June '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
July 2024
PE PREP SERIES |