We have a project which is on a steep slope (the bottom of the site is about 120 feet lower than the top of the site). If we attach a fire main to the bottom of the site, the fire pump we have won't have much issue with keeping the city pressure at a 20 psi minimum or above.
If we attach to the water grid at with the fire service main at the top elevation of the site, we will probably need a suction control valve in order to keep the city pressure at 20 psi at the top elevation since the available water supply is so low. My question is - if we pull pressure on a city's system at the low elevation, do we have to chart and consider the rest of the water supply network? There's a chance if we pull the water supply down to 20 psi at the lower elevation that the system at the higher elevations would be well below the 20 psi due to elevation pressure loss. Thanks for your input! Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe
4 Comments
Is the travel distance requirement for fire extinguishers in NFPA 10 measured like means of egress travel distance, or "as the crow flies"?
I've seen plans recently that just have a 75-foot radius around an extinguisher proving coverage and wasn't sure if that's the proper way to measure travel distance for extinguishers. Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe My daughter is in fifth grade this year and will be picking out a science fair project.
She really wants to choose a topic relating to fire sprinklers. Obviously, I'm doing everything I can to support this. I'm wondering if anyone out there might actually know of sprinkler-specific science fair projects that have been done in the past? Or maybe some ideas? Thanks! Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe Just wanted to wish each of you taking the PE Exam tomorrow all the best of luck.
I've enjoyed putting together these daily questions, the prep guide, and the online prep series and I very much hope that they've been helpful for you! If you ever have any comments or feedback, feel free to shoot them my way at [email protected]. Thanks for subscribing, commenting, and being a part of the community here. All the best in knocking this exam out tomorrow! What is the max gpm you can get with a 6” dr 18 underground?
We had a flow test of static 68 psi residual 48 psi flowing 1950 gpm. With 3111 gpm @ 20 psi. Some one is telling us the max gpm is 800 gpm. How is this possible? Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe I am currently dealing with a fire station that was constructed in 1965, prior to any adopted building codes in Indiana.
The fire station suffered structural and roof damage during a storm from a tree fall. My question is an exterior exit staircase from the second floor was damaged. A structural engineer assessed the staircase and addressed the items needing repaired, which is quite extensive and will need to be removed for repair. The staircase is far from meeting current code. The insurance company does not want to pay for a new exterior stairway that would meet code, they want to have it repaired. Is there any code requirement in the 2012 IBC that would require this stairway to be brought up to the 2012 IBC on an existing building? The stairway is the original. I cannot for the life of me find a code section that would require this stairway to be code compliant if removed and repaired. If we can cite a code requirement for this to be code compliant the insurance will pay for a brand new stairway, which is our goal. Any recommendations or prior experience with this type of situation would be greatly appreciated! (You would think the insurance would want a code compliant exit component, but I know its all about the $$$) Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe Determine the flow (in gpm) through an extended coverage pendent K16.8 sprinkler at 85 psi. a. 52 gpm b. 155 gpm c. 348 gpm d. 1428 gpm Solution | Posted 10/23/19
Is it acceptable to place the connection for the fire pump test header on the 'system' side of the isolation valve?
I've seen instances of this and it concerns me that there is a potential to render the FDC ineffective during pump testing; not to mention the possible corruption of pump test data due to the influence of the 'stored' water and pressure in the existing sprinkler system. Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe Here's this week's Prep Series leaderboard and the final one for the 2019 PE Prep Season. Be sure to check back this week for the plaque award winners that's based on the total season scores that have accumulated from each week. The Leaderboard lists the top total scores for the most recent three weekly exams for PE Prep Series participants.
See the entire scoreboard here. I'm designing a system with sprinklers at the ceiling of a large open space. There is a vestibule within this space that has a lower ceiling that requires 3 sprinklers. The client does not want pipe drops or hangers above the vestibule to be visible from the rest of the open space.
The proposed solution is to run a branchline down the wall and horizontal tight to the ceiling. Is there a good way to support this that meets the requirements of NFPA 13 chapter 9? The vestibule has CMU walls and metal stud ceiling. Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe A building owner has bought a large old warehouse and in about 6-8 months will convert it into educational spaces. They've asked if over the winter they could drain down the large wet sprinkler system as they aren't planning on heating the space or occupying the building during that time.
I recommended against it since they'd be without protection during that entire time and a fire could result in a total loss of the building. I also suggested they speak with their property insurer, couldn't store anything in the building, and would need to talk with the fire department as it would be a system impairment. Aside from that, what other barriers would they come across? What would you have recommended? Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe This project is a residential occupancy (dormitory) with a sprinkler system designed under NFPA 13. The contractor is using residential-style sprinklers within each unit, but standard-spray sprinklers in the corridor.
The corridor has these standard spray sprinklers just off the main which runs down the corridor. The contractor has provided calculations for the four most demanding adjacent residential style sprinklers, which is fine. He's also provided a calculation for the corridor using five sprinklers. NFPA 13-2016 11.2.3.4.2 states: 11.2.3.4.2 Where an area is to be protected by a single line of sprinklers, the design area shall include all sprinklers on the line up to a maximum of seven. Since the corridor's sprinklers are not residential, how many sprinklers should be calculated in the corridor? Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe This is giving me heartburn. A clothing manufacturing company wants to store group IV commodities.
16.1.3 Movable Racks. Rack storage in movable racks shall be protected in the same manner as multiple-row racks. 16.2.1.2 Protection Criteria for Rack Storage of Class I Through Class IV Commodities Stored Up to 12 ft in Height. 16.2.1.2.1 The protection criteria for storage up to and including 12 ft shall be the same as miscellaneous storage from Chapter 13. The definition of Compact Storage Module does not specify passive protection to qualify as such. My question is: “Is it correct to treat this rack configuration as moveable racks?” Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe Which of the following types of pipe would require the most hangers for the same length of 1-1/2" pipe? a. CPVC b. Copper Tube c. Steel other than Threaded Lightwall d. Threaded Lightwall Steel Solution | Posted 10/16/19
Have a flow test in a semi-rural area that has static pressures of over 130 psi but a residual pressure of 60 psi at just 500 gpm.
A flow test from nearly a decade ago shows worse results - with a static of around 120 and a residual of 20 psi at just 600 gpm. My initial concern with the older flow test was a partially-closed valve or obstruction in the line. With the newer test the residual pressure seems more reasonable, but other than something being wrong with the system is there a reason that would justify a residual pressure less than half the static at only 500 gpm of flow? Perhaps a system fed with small pumps and no tower? What are your thoughts? Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe The Leaderboard lists the top total scores for the most recent three weekly exams for PE Prep Series participants. See the entire scoreboard here. Want to join in? It's not too late - the PE Prep Series is the ultimate PE Prep tool. It's a series of 1-hour, 10-question simulated PE Exams offered weekly with solutions immediately following each exam. Learn more here. Every week of the series is retroactive so you can still test yourself with past week exams
NFPA 72 states that audibility from a fire alarm system is required to be provided throughout a building. Most jurisdictions are less concerned with attaining audibility in small, non-normally-occupied rooms such as janitor closets, small electrical rooms, or small mechanical rooms. However, several military reviews have pointed to exactly these rooms and asked how audibility is going to be achieved.
I typically provide speakers just outside of these groups of rooms such that there should be an achieved audible level, but how could I prove that during the design phase? Is there any calculation for audible loss through a door or software that could model this loss? I feel like there's a good handful of variables that play into whether audibility is achieved in these small rooms that may be difficult to predict. Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe Is there a complete list of points I need to monitor with fire alarm for a diesel driven fire pump?
I can't seem to find a comprehensive/definitive list in NFPA 20 or 72, but I would imagine at least one or more of the following would need to be monitored by code: fire pump running, primary sensor failure, low fuel level, main disconnect in "off" position, main disconnect in "manual" position, low pump room temperature, flowmeter left on, loss of AC power supply, loss of battery (load side of DC overcurrent), over-speed, and engine trouble (low oil, over temp, other?). Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe Which of the following would be considered a typical fire load for a bedroom? a. 0.4 - 0.8 lb/sqft b. 3.2 - 5.5 lb/sqft c. 11 - 14 lb/sqft d. 43 - 48 lb/sqft Solution | Posted 10/11/19
NFPA 13 (2016 Edition) Section 9.2.1.4.1 states:
9.2.1.4.1 Branch line hangers attached to metal deck shall be permitted only for the support of pipe 1 inch of smaller in size, by drilling or punching the vertical portion of the metal deck and using through bolts. The Sammy X-Press has listed hangers that call out attachment directly to metal deck for pipe up through 4" in some cases. From a code perspective, does the section above not apply, or would this be a code approved alternative? Just looking for the code logic that would allow use of listed special materials where the section above wouldn't trump this method. Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe I came across a specification requirement I've never seen before.
The specifications called for "sprinkler systems that require a fire pump to meet sprinkler requirements, all sprinkler pipe sizes shall be based on the Pipe Schedule method. This is to provide maximum sprinkler operation when the fire pump is not available, and minimizes the size of the fire pump. This also provides the possibility that with future water infrastructure improvements, the fire pump would no longer be required." A few questions about this - first, if the Pipe Schedule method could be used, wouldn't a fire pump not be necessary in the first place? Second, has anyone ran into something like this before and designed their system that way? For large facilities the only cost savings that comes back with having a fire pump is better pipe sizing. If that goes away, I could see the fire pump being a major cost burden above and beyond what it already is to the owner. Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe A fire pump's speed is altered from 1760 to 1800 rpm. What is the new head if the original was 120 ft? a. 115 ft. b. 123 ft. c. 126 ft. d. 128 ft. Solution | Posted 10/09/19
I have been asked to design a sprinkler system for a 4 story building as per NFPA 13R. The building has existing standpipes consisting of three 2 1/2” risers. I am hoping to use the existing standpipe risers to also feed the sprinkler system.
In this scenario would it make sense to include a hose allowance even though NFPA 13R does not require it? Also, since NFPA 13R doesn’t require zoning by floor, would it be plausible to have one single “Standpipe & Sprinkler Water Flow Alarm” at the water entry? I appreciate and respect your input. Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe Thank you to all forum contributors for September. We're continually seeing an uptick in interest and expertise, and I appreciate your willingness to encourage growth in our industry with your contributions! Here's the top commenters for September:
The Leaderboard lists the top total scores for the most recent three weekly exams for PE Prep Series participants. See the entire scoreboard here. Want to join in? It's not too late - the PE Prep Series is the ultimate PE Prep tool. It's a series of 1-hour, 10-question simulated PE Exams offered weekly with solutions immediately following each exam. Learn more here. Every week of the series is retroactive so you can still test yourself with past week exams
|
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop June '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
July 2024
PE PREP SERIES |