Is there any NFPA provision for forbidding a fire pump to start in the event a water storage tank has a water level that is too low?
I'm wondering what might happen if the water storage gets down to ~25% of the design level, or lower, and the potential need to shutdown the pump before it runs dry. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
11 Comments
James Phifer
9/2/2022 08:14:40 am
If the water supply can't meet 150% of the pump's rated pressure, then it must meet the greater of either 100% of its rated pressure or the maximum flow demand of the fire protection system.
Reply
Jesse
9/2/2022 08:21:22 am
Interesting question. The ramifications of a pump interlock to low water can't be understated.
Reply
Glenn Berger
9/2/2022 08:30:27 am
See NFPA 20 Section 4.16.9 and Section 4.17.10 and others. These references are from the 2019 version of NFPA 20.
Reply
Greg
9/2/2022 08:38:07 am
When viewing the fire pump as emergency equipment during and emergency, its purpose can be likened to a baseball analogy, where a batter has a runner on first and hits a pop fly ball, a sacrifice fly… the runner will advance. In the world of fire, sprinklers and fire pumps, when it’s all on the line, the fire pump is the batter. Sacrifice is a distinct possibility.
Reply
Alex
9/2/2022 08:42:40 am
When are you expecting the tank level to drop below 25%?
Reply
Tim
9/2/2022 08:45:11 am
The system would not be compliant to standards if automatic start prevention due to low level is introduced. I will suggest to install low water level alarms to trigger maintenance intervention.
Reply
schulman
9/2/2022 08:47:00 am
if youre not using the "handbook" versions of the codes with commentary you are doing yourself a disservice in my opinion
Reply
Chris
9/2/2022 08:48:21 am
There should be a low-water alarm that goes off at 4" below minimum tank capacity to meet system demand. And its always been my understanding that a pump is "sacrificial" and will either run until pressure is restored and the timer shuts it down, or the pump burns up.
Reply
Casey Milhorn
9/2/2022 08:54:22 am
https://www.zurn.com/products/fire-protection/pilot-operated-valves/zw215fp
Reply
Franck
9/2/2022 01:05:15 pm
The only alarm that is allowed to stop the pump is the overspeed with a diesel engine.
Reply
sean
9/2/2022 06:09:07 pm
no the code would rather it run dry and get what water it can the the fire the protect the pump
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop June '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
July 2024
PE PREP SERIES |