When are pressure reducing hose valves required on a dry automatic standpipe system?
I have a project where I have been asked to evaluate an existing sprinkler system for an 8-story apartment building. The original installation falls under NFPA 13/14/20 2013 edition. The building is served by four dry automatic standpipes and a separate wet sprinkler feed. The standpipes are not combination sprinkler/standpipes. The fire pump churn pressure is 212 psi and there is a pressure reducing valve provided for the wet system supply. There is no pressure reducing valve for the dry automatic standpipes. The hose valves on the standpipes are the pressure restricting type. Not pressure reducing. When reviewing the data sheets for the hose valves, it states "Adjustable restriction of pressures up to 175 lbs....at residual flow" but the valves themselves are rated to 300 psi. At normal, non-fire conditions, the standpipes have 23 psi static pressure of air, but if the dry valve were to trip for any reason, (non-fire or not) the standpipe exceeds 175psi static pressure on the 1st-7th floors. NFPA 14 2013 states that "7.2.3.2* Where the static pressure at a 21⁄2 in. (65 mm) hose connection exceeds 175 psi (12.1 bar), an approved pressure regulating device shall be provided to limit static and residual pressures at the outlet of the hose connection to 175 psi (12.1 bar)." Would the static pressure be considered the normal air pressure or the static pressure if the dry valve trips? My assumption here would be that the pressure restricting valve needs to be swapped for a pressure reducing type. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments
Anthony
5/16/2024 08:20:48 am
There are pressure regulating hose valves and pressure reducing ones. I intemperate 7.2.3.2 as requiring a maximum static pressure at 175 psi. I think to prevent initial blow back on the hose when the fire fighter opens the nozzle. This is a case where I'd use the corker 5500 SERIES NON-ADJUSTABLE PRESSURE REDUCING VALVE or the field adjustable one at the standpipe. Or I'd use a pressure reducing valve manifold as called for in 14 for 2 or more hose valves.
Reply
Steve Cooper
5/16/2024 09:33:10 am
In the snip of NFPA 14 above, it uses the word limit. When they use the word limit it makes me think they would want a pressure restricting since they don't want it going higher. But the pressure limiting valves I have seen limit 100PSI not higher.
Reply
Dan Wilder
5/16/2024 09:47:59 am
What was the originally approved installation? What has changed that would justify the change from the (assumed) approved installation? Section 1.3 for Retroactivity provides allowances to avoid having to change already approved and installed (correctly) systems.
Reply
GRAHAM N
5/16/2024 03:06:31 pm
The approved installation shop drawings show one detail of the standpipe with pressure restricting hose valves (with note: "typical for floors 1-7) and then the drawings also show a separate cross-section view of: building, standpipe, and static pressures with a note that pressure reducing valves are required on floors 1-7.
Reply
Jack G
5/16/2024 11:34:30 am
Agree that the valves should be changed out to prv s. The factory set type is ordered with the pressures of your specific jobs, however I prefer the field adjustable type that the fire department can adjust.
Reply
Casey Milhorn
5/17/2024 08:47:37 am
I agree with Jack on this one but also Dan to what is your exact scope? It sounds like you have been contracted to evaluate and make suggestions, and to Jacks point not a big fan of the factory set type of pressure restricting valves. That's a chance to suggest replacing these existing valves, maybe not from a code perspective but from a practical and possibly life saving perspective for the responding fire fighters.
Reply
Graham N
5/22/2024 04:02:26 pm
Casey,
Reply
Casey Milhorn
5/22/2024 04:37:42 pm
That makes sense and the fact that the existing pressure restricting valves are only listed for 175 psi should trigger a recommendation by you at the very least. I would be very careful with the install of a master PRV (which actually you would need to install 2 of them in series, with bypass assembly, as shown in NFPA 14). You might end up restricting the pressure to below 100 psi at the top @ 500 gpm. Not to mention these master PRVs can be unreliable (from stories I've heard). The field adjustable pressure regulating hose valves is probably the way to go. If you are not a PE or FPE, I would highly advise recommending that one be brought in to bless the changes. Just put it as an add price in your contract and if the owner elects to not pay for that option, that at least should reduce some liability on your part. This all sounds like a commonsense solution until the PRVs aren't tested and adjusted on a regular basis in the future and a firefighter and/or building occupants perish due to owners failure to maintain the system. But in this case, it does sound like the owner is interested in doing the right thing. Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop June '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
July 2024
PE PREP SERIES |