I am running into a lot of old systems that do not have hydraulic placard and some of them are old Pipe Schedule system.
Has anyone ran into an old pipe schedule system were the fire marshal is requesting hydraulic placards and if so has anyone found a way to satisfy the requirements without surveying the entire system and running new calculations? Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
9 Comments
7/17/2023 08:08:26 am
NFPA 25 2023 (and earlier) states: 5.2.5.2 A pipe schedule system shall have a hydraulic design information sign that reads “Pipe Schedule System.”
Reply
Glenn Berger
7/17/2023 08:23:34 am
I am in agreement with Matt. But before you put the placard on the system I recommend walking the system to see if the system is still in compliance with NFPA 13.
Reply
7/18/2023 08:39:57 am
Glenn - NFPA 25 does not require verification that an existing system meets NFPA 13. An NFPA 25 inspection is verification that the system is being maintained properly. Verifying the existing system meet the code it was installed under is outside the scope of NFPA 25.
Reply
Jason Carroll
7/17/2023 08:44:12 am
Once we have verified it is a pipe schedule system, we make a placard that states "pipe schedule system" as Matt mentioned and hang it on the riser. So far, we have not had any issues with it.
Reply
A. Wiseman
7/17/2023 08:52:31 am
I agree with Matt and Glenn. If you install a General Information sign in place of a Hydraulic placard, there is a place to indicate a pipe schedule system.
Reply
Dan Wilder
7/17/2023 08:58:54 am
NFPA 25-23' 5.2.5.2 -A pipe schedule system shall have a hydraulic design information sign that reads “Pipe Schedule System.”
Reply
Anthony
7/17/2023 09:16:05 am
A functional system does not need to meet current code it needs to meet the code it was installed at. I'm curious what your involvement is with an existing system and the fire marshal?
Reply
Jesse
7/17/2023 09:50:15 am
I would indicate which pipe schedule it was. OHPS / LHPS, or even a long time ago EHPS
Reply
Pete H
7/17/2023 12:44:44 pm
I like this. This seems like extremely relevant information.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop June '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
July 2024
PE PREP SERIES |