Does anyone know of a sleeve product that can be installed AFTER pipe installation without backing out the pipe?
The underlying issue is that I have a project with seismic requirements (for extra clearance at penetrations) that has many fire rated walls. Basic pipe sleeves with extra large clearance filled with fire caulk is our typical situation, but if a sleeve gets missed during rough-in, we're hoping to use something after that fact. So either looking for a split sleeve of some type, OR a way to fire caulk a 2 hour rated gypsum wall with extra large clearance per NFPA 13-2016 section 9.3.4.3. Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments
Pete H
4/22/2024 06:49:56 am
No idea if this is actually what you're looking for and I didn't check what it's actually listed for but:
Reply
Dan Wilder
4/22/2024 08:14:29 am
Talk to your firestop rep (Hilti, 3M), explain your wall (materials/thickness), hole diameter, split sleeve, and the rating and have them use an existing system or create an Engineering Judgement for the project to follow.
Reply
Glenn Berger
4/22/2024 08:35:23 am
The use of split-sleeves is what I have seen used in this application.
Reply
Adam
4/22/2024 09:22:58 am
Many UL listings allow a sleeve made of sheet steel that's rolled up and inserted into the opening. They often protrude from the wall a bit, and are held in shape by worm gears. Much like Dan's, but without the lock seam.
Reply
Jack G
4/22/2024 11:11:20 am
I always did pipe sleeve for seismic— solid usually galvanized, then I gave the drywall foreman a hundred bucks a t beginning of drywall to set, and a hundred more when job was done.
Reply
Jesse
4/22/2024 01:49:20 pm
I think I've seen some listed split sleeves
Reply
Scott
4/22/2024 07:05:25 pm
What about using Hilti fire collars? This would eliminate the need for caulking while addressing the large pass through holes. While fire collars aren’t typically required for water-filled metallic pipe, it may be easier in the long run. I have been on projects where it was actually cheaper to use the fire collars versus large amounts of fire caulk applied correctly. Just my opinion.
Reply