In NFPA 72, does Pathway Survivability apply only to Emergency Communication systems?
In the 2019 Edition of NFPA 72, Section 12.4 stipulates required protection regarding various levels. Section 24.3 Pathway Survivability defines requirements for different levels of declaration. Chapter 12 applies for all fire alarm wiring. However, the title of Chapter 24 is for Emergency Communication systems. Does pathway survivability apply only for Emergency Communication systems only? Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments
Pete H
8/24/2023 07:17:44 am
Please forgive my confusion, but NFPA 72 pertains to National Fire Alarm and Signaling Code. I'd think anything in NFPA 72 is emergency communications, because it's part of the fire alarm and signaling.
Reply
DS
8/24/2023 08:12:39 am
The section of NFPA 72:24.3 is addressing all emergency communication systems. This could be two-way wired in-building communications system, emergency voice/alarm communication system, mass notification, area of refuge, and elevator communications system.
Reply
Donovan
8/24/2023 08:52:23 am
Long and short of it yes, but if you use a control module or interface the SLC into the notification, your SLC loop now has to be 2 hour as well.
Reply
Todd E Wyatt
8/24/2023 09:35:36 am
SUMMARY
Reply
Robb K
8/25/2023 12:02:43 am
this may help . https://www.nfpa.org/News-and-Research/Publications-and-media/NFPA-Journal/2020/September-October-2020/In-Compliance/NFPA-72
Reply
robb k
8/25/2023 12:08:22 am
https://www.nfpa.org/News-and-Research/Publications-and-media/NFPA-Journal/2020/March-April-2020/In-Compliance/NFPA-72
Reply