We have an existing manufacturing area subject to NFPA 13-2022 Edition.
The Ordinary Hazard Group 2 manufacturing area sprinkler system can meet Figure 21.2.2.3.2 requirements for 0.20 density over 2,200 SF plus 500 GPM for hose streams required for Class III storage to 20 ft. high. Does the Ordinary Hazard Group 2 requirement of Section 4.3.3.2 (2) still limit storage height to 12-ft, regardless, since this is not a dedicated storage area? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
5 Comments
Pete H
4/16/2024 07:14:38 am
If you have 20'-0" high class III storage, the hazard classification isn't ordinary hazard group 2, it's High-Piled storage.
Reply
Glenn Berger
4/16/2024 08:11:50 am
The answer to your question concerning storage height in an OH2 sprinkler system is yes.
Reply
Jesse
4/16/2024 08:12:41 am
0.20 / 2200 isn't an OH2 density. But it is a density consistent with High Piled Storage. Whereas the manufacturing is OH2, the design density driver is the storage, and at 20-ft, this isn't misc. storage.
Reply
Chris
4/16/2024 09:11:02 am
The density is the same, but the classification is very different between OHII and HPS. Others are elaborating on many of these, but the one thing that can be added is that normal sprinklers are not rated for storage. If you use a typical K8.0 or K11.2, it usually isn't listed for use in High Piled Storage applications. You must find a storage-rated sprinkler, usually starting at K11.2. I believe that these calc the same as a normal head, just cost a small amount more. I assume they have some unique feature that makes them better at fighting storage fires than a traditional sprinkler? Somebody please add to this if able!
Reply
Richard
4/16/2024 10:03:24 am
Thank you Pete H for the way you broke it down.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop June '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
July 2024
PE PREP SERIES |