We have a project with a Class IV commodity rack storage area. The building has a roof slope around 24% (5.5 / 12). Based on NFPA 13 2022 Edition, Section 20.9.1, one option for this case is "where storage is protected with in-rack sprinklers in accordance with one of the options in Section 25.6, provided no storage is placed above the highest level of in-rack sprinklers." The question is: if a horizontal barrier and a level of rack sprinklers are installed above the last load level, and there is not going to be any storage above this level, can a system design be done based on 25.6 omitting the ceiling sprinklers? The gap between the top of the load and the roof is about 6.5 meters in the highest area. Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
9 Comments
Glenn Berger
12/19/2022 08:11:20 am
Got a few questions to be answered prior to giving an opinion.
Reply
Eric R
12/19/2022 08:49:46 am
Not having any ceiling level sprinklers at all seems like a pretty far stretch unless a full drop ceiling was installed at the bottom of the trusses. Especially with what looks like pretty wide aisles, I'd be worried that a fire starting in product left in the aisles would not have sufficient coverage from sprinklers in the racks.
Reply
Eric R
12/19/2022 09:08:00 am
Having a few more minutes to think about this, and I don't see any way ceiling sprinklers could be removed completely.
Reply
Franck
12/19/2022 10:18:03 am
The answer is definitely no.
Reply
Jesse
12/19/2022 10:46:52 am
In this case, I don't see you being able to omit ceiling level AS
Reply
Alex
12/19/2022 02:28:48 pm
As others have mentioned above, I do not see a way to omit ceiling sprinklers here.
Reply
12/19/2022 05:19:21 pm
I agree with all, never leave out the overhead sprinklers.
Reply
Alan Larson
12/21/2022 01:58:26 pm
Look at Section 25.8. If the top of the rack had a horizontal barrier with the first complement of in-rack sprinklers directly below that barrier, with in-rack sprinklers placed appropriately from there towards floor level, what would the ceiling level sprinklers be protecting? I realize the notion of no sprinklers at the roof deck is novel, but it seems this section may allow that.
Reply
Eric R
12/21/2022 07:21:43 pm
My intent is for this to come across in the spirit of good natured debate!
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop June '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
July 2024
PE PREP SERIES |