I have a 5-story building going up with 4-story residential over 1-story parking.
Can the residential portion be NFPA 13R? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
9 Comments
Pete H
7/23/2024 07:14:11 am
Unfortunately this leads to more questions:
Reply
Anthony
7/23/2024 07:19:20 am
Potentially if you have a pedestal building. which requires a 3 (or 2?) hr horizontal fire separation between the first floor parking and the remaining R occupancy. Mix of ch 504 and 510 of ICC.
Reply
Todd E Wyatt
7/23/2024 08:25:49 am
The scoping Code (e.g. IBC-2021) identifies where an automatic sprinkler system (ASPS) is required based on the Occupancy Classification(s) (OC) assigned to the building and/or “Specific Building Areas and Hazards”.
Reply
7/23/2024 08:41:58 am
It depends.
Reply
Jonathan Griffin
7/23/2024 10:47:09 am
No. With a Parking Garage directly below the R Occupancy, the Garage now needs an NFPA-13 system. Based upon the information provided, the chances of the highest Floor Landing being above 30-Ft. are good.
Reply
Jack G
7/23/2024 01:39:15 pm
A lot depends on the building so let’s review some things:
Reply
Jack G
7/23/2024 01:50:53 pm
The paragraph that starts with “ so if should be amended to :
Reply
Joe Burtell
7/25/2024 08:51:03 am
Per the 2021 IBC If you building to the top floor is mor than 30 feet above FD access, 13R is not allowed. This is new to the 2021.
Reply
Jack G
7/25/2024 10:03:46 am
The building height can be increased in height due to the type of construction 1-A, 2-A , etc.