I'm reviewing a single-family home NFPA 13D system.
What is the proper way to calculate a 13D system? Is this a 2- or 4-sprinkler calculation? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments
Alex
9/7/2021 07:28:03 am
Hi Anonymous,
Reply
Alex
9/7/2021 07:29:12 am
Correction, “up to a maximum of two sprinklers”!
Reply
JIm
9/7/2021 08:06:56 am
NFPA 13D - .05 for 2 hydraulically most demanding.
Reply
Jesse
9/7/2021 08:16:20 am
2016 NFPA 13D 10.2.1 The number in the design area shall be all of the sprinklers within a compartment, up to a maximum of two sprinklers, that require the 0greatest hydraulic demand.
Reply
Brian Cockburn
9/7/2021 09:14:43 am
As others have said, up to two sprinklers in a single compartment. If you don't have any compartments with two sprinklers and you want to be conservative; you could do two calculations with the two most remote individual sprinklers. That would give you more confidence in your design.
Reply
Dorgan Trostel
9/9/2021 05:09:39 pm
I like to max spacing in bedrooms where one 20x20 spacing spk will cvr the room where 2 might be needed with smaller coverage but also to get away from pesky ceiling fans.