We have a fire pump room with three 75 HP main pumps that operate sequentially depending on the flow required.
Can we install all 3 controllers within a single enclosure? If not, what standard, code forbids this? Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments
Glenn Berger
7/14/2023 08:09:20 am
The pump controller is a listed unit, by the manufacturer.
Reply
SCHULMAN
7/14/2023 09:21:52 am
Quick look at NFPA 20 ... seems as if the requirements for enclosures "assumes" or "suggests" a single controller per enclosure but doesn't really state it ...
Reply
Pete H
7/14/2023 09:32:23 am
I'm with Glenn and schulman, I can't see a direct code reason against in NFPA 20, so if you can find a listed and approved multi-pump controller enclosure, go for it.
Reply
Anthony
7/14/2023 09:45:31 am
The controller should come in its own enclosure or box that generally is floor mounted and the whole assembly is listed.
Reply
Dan Wilder
7/14/2023 02:15:41 pm
As Glenn said, controllers are listed individually by ANSI/UL 218, ANSI/UL 508, UL347, and follow NFPA 20 & 70. If there is any modification of those enclosures, the listing/approvals are voided.
Reply
Jesse
7/17/2023 07:46:02 am
I'm dealing with a similar issue. I've not ever seen multiple controllers in one enclosure.
Reply
Jerry Clark
7/17/2023 10:33:31 am
Based on the responses, this sounds like a grey area that has never been addressed. The one cautionary thought I had was all your eggs in one basket. Lose one controller to a short, may lose all of them. I would stick with individual controller cabinets based on that scenario.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop June '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
July 2024
PE PREP SERIES |