I have an S-1 occupancy. It is a privately owned storage unit (no public access) used for the storage of exotic cars, maybe 3 vehicles in total. The space is about 1,400 square feet, and is fire sprinkler protected. There is a wood-framed mezzanine at the back of the unit as is about 300 square feet.
The question that has come up is if the underside of the open wood stairs to the mezzanine needs to be protected with fire-retardant gypsum board? There is no sprinkler coverage under the stairs. The mezzanine may be built out by the owner to have a few chairs, a couch, a television, etc. Digging into the code talks a lot about accessibility but not so much about the fire resistance requirements for the stairs. I have the found following in the 2015 IBC (code we are under): 1104.4 Multistory buildings and facilities. At least one accessible route shall connect each accessible story and mezzanine in multilevel buildings and facilities. Exceptions 1. An accessible route is NOT required to stories and mezzanines that have an aggregate area of not more than 3,000 square feet (278.7 m2) and are located above and below accessible levels. This exception shall not apply to: ...and... 4. Where a two-story building or facility has one story or mezzanine with an occupant load of five or fewer persons that does not contain public use space, that story or mezzanine shall not be required to be connected by an accessible route to the story above or below. So...the accessibility issue is covered but nothing about the rating of the stairs that I can find. Any help would be appreciated. Maybe I am not looking in the correct code section. Thank you! Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments
Pete H.
3/10/2022 07:13:38 am
Okay, beyond IBC, what nfpa standard were the sprinklers in the building installed? I'm assuming NFPA 13 (I'm using 2016 edition, but I think you might be in 2013 due to your edition of IBC being 2015, so you may want to check that). because despite being private, this hasn't been described as residential.
Reply
Jesse
3/10/2022 09:05:40 am
The lack of protection under the stairs combined with the lack of a fire barrier is concerning. I would imagine the stair way creates a shielded area to ceiling level sprinklers - and would continue to do so even if gypsum was installed.
Reply
Alex
3/10/2022 09:06:02 am
Hi,
Reply
Todd Wyatt
3/10/2022 09:36:30 am
The adopted IBC (or IRC) is the starting point to determine the scoping requirements of the automatic sprinkler system (ASPS) per the "addition" of the mezzanine. You referenced the 2015 IBC.
Reply
Gregg Peterson
3/10/2022 01:14:27 pm
Thank you (and other commentators) for your in-depth research.
Reply
Little Fire Squasher
3/10/2022 04:04:01 pm
Here are some things that might trigger sprinkler:
Todd Wyatt
3/14/2022 09:14:14 am
A. Unless the steel joists include Sprayed Fire-Resistive Material (SFRM), the Type of Construction is probably Type IIB Noncombustible, Nonprotected.
Gregg Peterson
3/14/2022 03:59:18 pm
Thank you to everyone for the well-though out responses. This forum is truly one of the web's best resources...and Todd, received some more information on Friday that any owner driven modifications will need to be reviewed and permitted, including any upgrades to the open wood framed stairs and mezzanine that were previously approved for the "shell" space.