Hi all, what is the maximum length of the connection from the hydrant to the fire water main?
NFPA 24 mentions that the minimum size is 6" but couldn't find anything related to the pipe length. Thanks Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments
Franck
5/3/2024 08:17:13 am
No limitation as long as the friction losses are not too important because of the length...
Reply
Chuck
5/10/2024 07:27:50 am
Nice job !
Reply
Fred Walker
5/3/2024 08:18:30 am
There is no code or standard driven maximum length for a lateral between the water service main and a fire hydrant. There are the practical limits of hydraulics to obtain the desired flow at the hydrant.
Reply
Jesse
5/3/2024 08:19:36 am
There is no max length.
Reply
Todd E Wyatt
5/3/2024 08:37:05 am
IFC-2021 Appendix C Table C102.1 REQUIRED NUMBER AND SPACING OF FIRE HYDRANTS identifies the minimum number of hydrants based on the Fire-Flow Requirements (gpm), the average spacing between hydrants (feet), and the maximum distance from any point on street or road frontage to a hydrant (feet).
Reply
Anthony
5/3/2024 08:38:46 am
As all have said, no there isn't a limit. However, consider the application, if this hydrant is going to feed a manual standpipe you may want to use 8'' instead of 6''. Those friction losses can add up with a tight curve.
Reply
Jack G
5/3/2024 09:39:48 am
Check out the ibc and Nfpa 1 also for guidance.