Does a standalone mass notification system (MNS) require a smoke detector in front of the panel for a drug reduction facility?
The facility is 2,100 sqft and houses a minimum of 11 persons. Basically a drug testing and counseling facility. No Fire Alarm required for the building; being governed by UFC 3-600-01 for the US Air Force. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments
Glenn Berger
7/4/2024 08:24:13 am
Look at Section 10.4.5 -
Reply
Kim Watson
7/4/2024 09:45:09 am
I would think a standalone MNS is just a glorified PA system.
Reply
Jack G
7/4/2024 04:51:28 pm
I m with Glenn.
Reply
Sean H
7/5/2024 03:22:53 am
Excerpt from 2022 edition of NFPA 72 below and shows latest intent. Verify adopted edition in your jurisdiction however.
Reply
Jordan
7/5/2024 03:47:20 am
You may want to discuss with the DFPE about providing a combination fire alarm/mass notification system. Although technically a fire alarm system might not be required you’d be providing a few extra initiating devices (e.g. manual pull station, smoke) to the system/matrix and call it a day.
Reply
Ricardo Gonzales Jr
7/8/2024 08:38:13 am
In this case. A sprinkler monitoring system does not require notification in the building.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop June '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
July 2024
PE PREP SERIES |