What are your recommendations for fire safety of single height storage of Lithium-ion vehicle batteries?
Currently in our warehouse, in a sprinklered covered area, we are storing 3 to 5 of these lithium-ion batteries before they are sent to dealerships. We have security guards take 1-hour temperature readings throughout the day and night but little else has been put in place and a proper fire risk assessment has not been performed. Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
9 Comments
Mike
4/28/2021 08:27:01 am
I am working on a massive project where there are massive quantities of these types of batteries being manufactured, stored and used. The owner had a Fire Protection Engineer prepare a risk assessment.
Reply
Thomas
4/28/2021 08:31:03 am
What design density? How high?
Reply
Dan Wilder
4/28/2021 08:44:03 am
NFPA 855 has a little guidance available.
Reply
CJ Bonczyk
4/28/2021 09:17:22 am
I agree with Dan. We have had these facilities pop up all over Texas. Many times the information regarding the storage layout, height, if they are contained or not, all needs to be long thought out prior to the sprinkler design and water availability. Currently NFPA 855 2020 is your go to for now. Hiring an FPE and heavy coordination with the AHJ must happen to properly CYA. We have had to use certain clean agents, revise storage and add cut off spaces. The water usage to suppress a fire of these type is immense. A single instance here in Texas involved a Tesla car that the batteries caught fire and majority of the damaged was caused in the first 10 minutes from the batteries and chain reaction and just to put the car fire out required almost 30k gallons of water.
Reply
Franck
4/28/2021 09:35:50 am
There is a difference when the batteries are being used (ESS) and then you can apply NFPA 855 (0.3 gpm/ft² based over the area of the room or 2500 ft²) and storage of batteries that are not being used (such as big storage facility).
Reply
Vasu
1/4/2024 10:06:27 am
What are the criteria to store large quantities of Li battery pallets on the floor?
Reply
Franck
4/28/2021 09:39:12 am
If batteries (lithium ion) are being used, then you may consider the following.
Reply
Franck
4/28/2021 09:40:16 am
Safety precautions
Reply
Franck
4/28/2021 09:42:32 am
Used/damaged battery disposal