I have seen this method of arranging fire suppression components (see attached schematic) several times where I live. The attached is a partial re-creation of the fire water entry schematic for a high-rise building with a fire pump. The system has low and high pressure zones. The underground parking dry systems are served by the municipal water directly, and the standpipes and aboveground sprinklers are fed by the pump. Questions: 1. Can you have a FDC serving the low pressure zones as shown on the suction side of the pump per NFPA-14 6.4.3.1? 2. If not, how should the schematic be arranged instead? 3. What could happen if the Low Pressure FDC were pressurized as shown? This project was built under the 2013 editions of NFPA-13, 14, and 20. I am asking because I am beginning design of a sprinkler system for a 22 story high-rise. Thanks for your help. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
9 Comments
Anthony
5/6/2024 07:36:11 am
1. No
Reply
OP
5/6/2024 09:59:09 am
Thanks, Anthony. To clarify - the schematic shown is for a previous project that's only 13 storeys, and I wasn't the designer. The 22 storey building is a new project that I will be designing.
Reply
Anthony
5/6/2024 08:04:23 am
So the part 3 was bugging me and looked it up in the 2019 handbook:
Reply
JI
5/6/2024 08:24:08 am
In order to have a low pressure zone like that, the entire subheader for P2 & P1 should be subdivided with a check valve to ensure it cannot feed the suction side of the fire pump.
Reply
OP
5/6/2024 09:59:58 am
That's generally what I'm thinking for my 22 storey project. Thanks!
Reply
chad
5/6/2024 08:42:23 am
It is common to have the garage with a separate FDC in many larger metros in colder climates with mid and high rises. How does the FD regularly operate?
Reply
Dan Wilder
5/6/2024 08:59:37 am
Missing some info here but my thoughts:
Reply
Casey Milhorn
5/6/2024 09:15:57 am
Anthony has the code reference and no it is not allowed. JI has the proper solution if you want to keep low pressure zone, or Anthony if you want to have just one pressure zone. You can also use a master PRV to reduce pressure for wet and dry risers, if you are using it for standpipes you will need to provide (2) master PRVs in series w/ bypass. Depending on the applicable code and standard, (2) FDC's for each zone may be required as well. That would make the two pressure zones even more expensive vs the one. Also make sure to check the pumping ability of the responding FD. Sometimes redundant pumps are required if above the ability of the FDC to get 100 psi @ 500 gpm.
Reply
Jack G
5/6/2024 11:06:19 am
1. No, not legal.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop June '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
July 2024
PE PREP SERIES |