We are having problems getting a flowmeter to accurately read the flow rate that matches what we are measuring downstream out through a test header. A reading using calibrated pitot gauges outside at 1,500 gpm, for instance, is showing 1,900 gpm on the flowmeter inside.
Military specifications for the project require that the flowmeter read accurately, and that the system be piped such that flow must go through the flow meter out through the pump test header. The flowmeter manufacturer has recommended using a stream straightener upstream of the flowmeter to better streamline the flow through the meter and get more accurate readings. Does anyone know of a stream straightener that could be used in a fire pump test loop arrangement? I would think it would have to be listed, but that's just a gut feeling. I don't currently know of any listed stream straighteners. We generally need to meet the black and white code and specifications mandates spot-on without any code alternatives, if possible, being that it's a military project. Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
10 Comments
Pete
8/13/2021 06:45:17 am
Crestar's line of stream straighteners seem to be made for firefighting equipment and are "NFPA 1964 compliant", but I don't see a UL listing on them.
Reply
OP
8/13/2021 07:41:33 am
We probably wouldn't be able to get approval on anything outside the spec unless it was our only option. It's been very black and white to the spec to date.
Reply
Alex
8/13/2021 07:34:23 am
Hi Anonymous,
Reply
OP
8/13/2021 07:44:28 am
Right! It's been a tough project for sure.
Reply
Alex
8/13/2021 08:34:39 am
I will keep an eye out for a stream straightener to fit in your case but sadly haven't heard of one. Maybe the manufacture can recommend one since they are guiding you to go in that direction?
Dan Wilder
8/13/2021 07:58:23 am
I would recommend pulling the flow meter and send it in for calibration.
Reply
OP
8/13/2021 08:10:45 am
All good questions - thanks Dan.
Reply
Dan Wilder
8/13/2021 08:26:50 am
I have also had luck increasing the size of the supply side of the flow meter (before the 5 diameters of straight pipe) and using a concentric reducer (don't forget a means to vent the trapped air) making kind of a reservoir for the turbulent water to calm a bit. Most of my riser rooms weren't that big but got lucky on one to be able to try it.
Brad K
8/13/2021 02:46:28 pm
I agree with Dan. We have seen these flow meters perform poorly and be corrected with calibration by the manufacturer.
Reply
John G
8/13/2021 08:37:29 am
All good answers. I put an air relief on my flow meter systems, nfpa 20 has a diagram, that seems to even the stream out. At the highest point.
Reply