I was recently cited by a surveyor for not having supervised control valves (isolation gate valves) on the jockey pump.
All other control valves are supervised for the riser and fire pump. I view the jockey pump as not critical or a necessary part of the fire pump and would not have an adverse effect if the jockey pump were out of service for any reason. Is there a NFPA code reference that requires supervision on jockey pump gate valves? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
13 Comments
Alex
12/27/2022 06:14:09 am
Hi,
Reply
Aric Alexander
12/28/2022 07:23:27 am
Alex, thank you for the response and specific code reference. Take care
Reply
Franck
12/27/2022 08:17:13 am
As indicated by Alex, no need for supervision.
Reply
Aric Alexander
12/28/2022 07:24:25 am
Franck, great explanation. Thank you
Reply
12/27/2022 08:29:38 am
I'm glad Alex was able to provide IBC reference, so you'll have that to go on.
Reply
Aric Alexander
12/28/2022 07:26:05 am
Matthew, although the IBC is helpful, the survey I was under referenced NFPA and I very much appreciated your response. Thank you
Reply
Kyer
12/27/2022 09:07:22 am
Remember to check with your local AHJ and confirm what codes and standards they have adopted. The AHJ may have special requirements that require you to go above and beyond the standard.
Reply
Aric Alexander
12/28/2022 07:30:19 am
Kyle, this specific survey was a Joint Commission consulting survey, not an AHJ. This individual saw a “control valve” and got excited to find a violation :) , not knowing what the code states about this item. This system has been installed for over a decade. I really appreciate you taking the time to respond. Take care
Reply
Edgar
12/27/2022 10:15:00 am
CMS and Joint Commission surveyors are quick to cite, a code reference should be provided for any deficiency noted, No code reference = no deficiency.
Reply
Aric Alexander
12/28/2022 07:32:22 am
Edgar, AMEN! Absolutely correct. This item was cited under a general reference regarding suppression systems in his report. Nothing specific, which made me look deeper and ask this question. Thank you for your response!
Reply
Jack G
12/28/2022 10:56:54 am
It’s been my experience to check with the AHJ.
Reply
sean
12/31/2022 08:45:41 pm
i always think of any valve controlling the water supply to the heads needs supervision not every one that controls flow
Reply
Peter Apgar
1/5/2023 12:51:40 pm
After reading this article, I promptly locked our jockey pump valves in open position. Makes sense. However, directly next to the jockey pump is the electrical disconnect, a large scissor switch. Another room has the breaker for the pump. Neither of these disconnects are supervised or locked out. I don't see any reference for doing so, but seems just as important as locking valves on. Just thinking out loud.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop June '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
July 2024
PE PREP SERIES |