NFPA 13 (2022) states; "Sprinklers shall be installed under all exterior projections greater than 4 feet where combustibles are stored."
I have a retail building and the occupant desires to sell (combustible) merchandise outside their store, under the canopy. The projection greater than 4 feet. My question is related to the term "stored." Is this defined anywhere? The combustible materials are under the canopy during business hours, but brought inside the store when the store is closed. Is the display of products under the canopy considering "storing" them? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
16 Comments
Pete H
11/17/2021 06:49:17 am
Best I can offer you is NFPA 101 (2018 ed.) 6.1.13.1 restates a part of chapter 3 in NFPA 101 that defines a storage occupancy as "An occupancy used primarily for storage or sheltering of goods, merchandise, products, or vehicles."
Reply
Dan Wilder
11/17/2021 06:52:19 am
This is one of those "choose your battles" moments, unless you're just playing middle man between an owner and the Fire Marshall.
Reply
Alex
11/17/2021 07:11:46 am
I think Dan has this spelled out perfectly. No, there is not a specific definition within NFPA that you can resort too. I would have to agree, shrink the canopy to be less than 4' or add protection.
Reply
Jesse
11/17/2021 08:12:59 am
"Stored" isn't defined in 13 per se. However, we more or less universally consider combustible material present under a canopy or overhang 4-ft or greater to require protection. In this case, its a retail occupancy with a pretty constant fire load under the canopy.
Reply
Anthony
11/17/2021 08:16:49 am
Reply
Mikr
11/17/2021 08:29:12 am
If it's not a transient load i.e. removed daily into the warehouse and stays repeatedly or overnight, it's storage. A loading Dock has transient loads that remain only temporarily.
Reply
CJ Bonczyk
11/17/2021 08:59:25 am
Since your projections are greater than 4', the projections are not separated from the building regardless if they are non combustible or combustible, by the black and white standard NFPA requirements, sprinkler protection is required. Rules of NFPA 13 9.3.19 specifically A.9.3.19.2 apply in this situation stating that you have to comply with NFPA 13-9.2.3 for exterior projections.
Reply
Ronnie Morales
11/17/2021 09:07:33 am
No. You must apply Merriam-Webster’s Collegiate Dictionary, 11th edition. Here's a link for future reference.
Reply
Brett
11/17/2021 09:09:45 am
Your best bet is to consult the AHJ. At the end of the day, they
Reply
Franck
11/17/2021 10:22:49 am
Normally, if you ask the question, you already have the answer...
Reply
Todd Wyatt
11/17/2021 10:30:07 am
I have had AHJs identify waste receptacles that are under nonsprinklered exterior projections as "combustible storage" which would require sprinkler protection. The solution was to relocate the waste receptacles from under the projection.
Reply
Robert Bambino
11/17/2021 10:33:48 am
I would say if this "storage" is out under the canopy on a regular basis and between regular hours, than it get protected. I would go so far as saying even if it was used for loading and unloading, protect it. That is from an AHJ stand point.
Reply
Jon Nisja
11/17/2021 06:07:40 pm
I work for the Minnesota State Fire Marshal (MSFM( Division. We had an appeal a couple of years ago regarding trash containers in the corridor of apartment buildings pending their removal. Our state fire code prohibits combustible storage in corridors.
Reply
FM
11/19/2021 09:57:27 am
After the second time of asking nicely to remove the refuse cans from the hallway, the property owner and manager would be in cuffs heading to our local jail. Never overcomplicate issues that are not complicated in the first place, lol.
Reply
sean
12/31/2021 06:47:25 pm
if a term is not defined in the standard, you can use the code, or common usage (dictionary)
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop June '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
July 2024
PE PREP SERIES |