If an existing building has a pipe schedule system that is determined to be "extra-hazard", without any design information, would that system be equivalent to an Extra Hazard Group 1 hydraulically-calculated design curve of 0.30 at 2,500 sqft?
Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments
Alex
11/2/2021 05:32:50 am
Hi,
Reply
Anthony
11/2/2021 08:24:07 am
Depends what equivalent means in this case.
Reply
Jesse
11/2/2021 08:34:38 am
Great question. The short answer is probably "yes". The EHPS was intended to provide an EH1 density. Now of course, if using 2016 NFPA 13, we can't even modify an EHPS system without calculating it per 23.7. So, my recommendation is take the extra time and steps to calc the system to be sure it is hydraulically adequate to do what you expect to do.
Reply
Dan Wilder
11/2/2021 08:37:26 am
This one I'm going to disagree with. This is two separate design approaches and while they accomplish the same end result for allowable design, I would not interchange the two.
Reply
franck
11/2/2021 10:05:55 am
Not necessarily.
Reply
Joshua Freedman
11/2/2021 10:18:00 am
I would say although it is possible, most often times it is not. I am an inspector and have seen many pipe schedule systems over the years that have been hydraulically calculated later to determine it's actual design, and as a previous commenter stated, it is highly dependent on pressures available, as well as pipe diameter installed. Most Extra Hazard pipe schedule systems I have seen calculated, or have calculated myself, usually come up around 0.15 - 0.20 / 3000, around an OH2 output. An option you might look at that I see sometimes is installing a fire pump on the system to boost the pressures up - with fire pump installation I have seen pipe schedule systems get into the 0.33 - 0.45 range.