Are the requirements for sprinklers in an 'Extraction Booth' the same as a 'spray booth'?
I have a customer looking to add wet pipe coverage to their new 'solvent extraction booth' which appears to be the same as a paint spray booth. The customer is claiming that the AHJ told them that there is no requirement for a separate riser as it's not technically a paint booth. I can't find any supporting documentation of this in any NFPA standard. The closest example I can find is a paint spray booth which appears to require a dedicated riser no matter what. Anybody have any experience with this? Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
5 Comments
Pete H
11/3/2023 08:04:23 am
Not speaking out of experience, but I did a quick google.
Reply
Glenn Berger
11/3/2023 08:32:05 am
I cannot speak for a "extraction booth," but the if the issue is whether you need a dedicated isolation valve and flow switch then you should be able to convince your client of the benefits of providing such an assembly for your application.
Reply
Anthony
11/3/2023 08:52:54 am
Ask what their process is. If it's a spray application, then you have a paint booth with ducting removing fumes from an environment. You might need to have sprinklers in that venting duct if you're derailing is explosive hazards and aerosolized accelerants, NFPA 45 I think for that? "extraction booth" is not a defined technical term in NFPA.
Reply
Franck
11/4/2023 05:29:28 am
To complete Glenn's comment...
Reply