I am looking at a project that shows 6-inch underground lead-in to a riser room. The specs however call out the install of a 1,000 gpm pump. NFPA 20 shows that for a 1,000 gpm pump suction sizing should be no less than 8-inch diameter.
Is a 6-inch even allowed for this application? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments
Jay Richardson
9/6/2021 08:13:25 am
The minimum suction size of 8in is required only for 10 pipe diameters (80 inches) upstream of the pump suction flange, to reduce the water velocity just prior to entering the pump. Yes, your underground is permitted to be 6in supplying a 1000 gpm fire pump, up to 80 in before the suction flange.
Reply
Glenn Berger
9/6/2021 08:14:18 am
The 6 inch pipe will probably be too small for a 1000 gpm pipe. With a 1,000 you will need to test the pump at 1500 gpm (150% of pump rating, there are limited exceptions to this rule).
Reply
JON DIMANLIG
9/6/2021 08:20:56 am
Per NFPA 24, Pipe smaller than 6 in. (152.4 mm) in diameter shall not be installed as a private service main supplying hydrants. So you may increase you pipe diameter based on the pump flow capacity
Reply
Jesse
9/7/2021 07:26:53 am
I agree with Jay. But my concern is more regarding the 150% flow and the ability of the 6" to supply it.
Reply
Alex Riley
9/7/2021 08:48:17 am
HI Anonymous,
Reply
Casey Milhorn
9/7/2021 09:14:17 am
Yes, what Jay said. BUT, make sure it works hydraulically in your calculations as well. The pump not meeting 150% is not grounds for failure at commissioning or future fire pump testing (to my understanding).
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop June '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
July 2024
PE PREP SERIES |