We have an NFPA 13 commercial project.
Do you allow a domestic water tap coming from an NFPA 13 fire sprinkler riser? If it is allowed, what provisions should I be looking for when reviewing a layout with this arrangement? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
16 Comments
Anthony
4/4/2023 07:03:55 am
No, this would lead to cross contamination issues. IE gross sprinkler water and cutting oil in the water supply. This 100% should NOT NOT NOT be done to an existing system.
Reply
Jesse
4/4/2023 08:06:09 am
It depends. I've seen numerous times where the tap to domestic is upstream of the riser backflow preventer device. This isn't uncommon at all, and not just on 13R system but 13 as well.
Reply
Brad K
4/4/2023 08:22:19 am
As Jesse said, we see it often upstream of the backflow. It needs to be approved by code officials and the sticking point is this needs to be a metered supply from the municipality. Lots of fire lines are not required to be metered.
Reply
Alex
4/4/2023 10:29:42 am
Sean covered it. If its before the DCVA, its a combined service. downstream from the check, you are now drinking lovely sprinkler water!
Reply
Glenn Berger
4/4/2023 08:08:08 am
Domestic connections to the Fire Service is not permitted. Depending on the locality, Industrial connections to the Fire Service may be permitted.
Reply
Dan Wilder
4/4/2023 08:23:14 am
I've seen it on existing buildings however the potable piping configuration was specific to Potable piping types (Ductile iron above ground) but we had to place (or add) a reduced pressure backflow prior to changing to standard steel piping to keep the non-potable separated from the potable.
Reply
James Evans
4/4/2023 08:24:24 am
There is such a monster as a circulating fire sprinkler system. You will usually find them in dwellings and piped with PEX. These systems combine all cold domestic and fire water services into one system. It is unusual but can be done.
Reply
Josh
4/4/2023 08:33:41 am
Some of the AHJs and utilities I've worked with throughout the country have required the domestic tap come off the underground fire main into a vault where the backflow and meter is.
Reply
anon
4/4/2023 08:55:33 am
Should domestic demand be added? Why or why not
Reply
Josh
4/4/2023 09:00:41 am
I could be wrong on this, but I would think if you tap off your fire main upstream for a domestic line, you would need to subtract the demand of the domestic throughout the building from your available pressure and flow. Unlike us, who hope to never have water start moving through our pipes, the domestic people are going to be hitting peak demand times and days. Not being prepared for that if a sprinkler sets off in your most demanding area and you learn you don't have enough pressure to sprinkler the building would be a bad day.
Reply
Chad
4/4/2023 12:04:31 pm
For a 13D yes, its 5 GPM, flat rate.
Reply
Casey Milhorn
4/4/2023 09:03:59 am
As others have touched on, it depends on where the tap occurs. At base of riser, before a backflow preventer? After the fire protection backflow, flow switch, etc?
Reply
Todd E Wyatt
4/4/2023 09:11:22 am
2021 NFPA 13 references “DOMESTIC” per the following :
Reply
Todd E Wyatt
4/4/2023 09:11:51 am
REFERENCES
Reply
Todd E Wyatt
4/4/2023 09:13:00 am
REFERENCES continued ...
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop June '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
July 2024
PE PREP SERIES |