Is there a set allowance on the fitting angles for sprinkler aboveground pipe? I'm reviewing a couple of projects where I find bends similar to the example below. The designer is using different pipe angles for reticulations. I'm wondering if there is a clause that prohibits such a use.
Appreciate your insight & feedback. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments
Pete H
10/18/2023 06:49:27 am
Typically elbow fittings are only going to come in 90, 45, and 22 degrees.
Reply
Dan Wilder
10/18/2023 07:51:25 am
11¼° elbows are available, toss in a couple flex vics and you can get another degree or so with a roll groove, cut groove gets it a little further (just remember for deflection angles shown typically need to be reduced 25-50% for design depending on size).
Reply
Dave
10/18/2023 01:45:56 pm
For unique angles some contractors (you know who you are) sometimes prefer custom-welded elbows (or combinations of elbows) rather than couplings and odd elbows. Either in-house fabrication or outside fab. Especially if you are hitting beam penetrations. Nothing wrong with it, it is hard to say if this designer knows what he/she is doing or if it's going to be be a nasty fitter (or lister) call, lol. Hydraulics calcs need to be considerad as well.
Reply
I suspect this is drawn in Revit or another 3D modeling tool where bends of any angle could be allowed. As all the guys have said, we are looking at 90, 45. 22-1/2 & 11-1/4 degree fittings, or 2 elbows to get whatever angle you like and 3 to get under stairs. I see so much that FP engineers don't do the drawings who would be fully aware of this. Pre-fabricated fittings are costly and cut & shut on site is completely out of the question for me.
Reply
Anthony
10/18/2023 08:19:39 am
Revit allows you to 'create' fittings to make odd angles work that don't have a solid relationship with reality. So I would guess this is an instance of inexperience?
Reply
David Kendrick
10/18/2023 08:26:53 am
Short answer is if you can purchase it from a manufacturer that follows industry standards outlined in the NFPA fire protection documents you can use the fittings.
Reply
Glenn Berger
10/18/2023 09:42:08 am
Basically agree with all above comments. I have spoken to the CADD (or now VDDS) group at work. Just because the program can detail items to .0000001 inch, that is not going to happen in the field. Engineers and Engineering Technicians need to push back on these updated computer generated designs.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop June '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
July 2024
PE PREP SERIES |