![]() My understanding is that sprinklers are not required in a commercial warehouse that was constructed prior to the code requiring them. So, how would a requirement apply regarding Open Rack Storage and Closed Rack Storage and the requirement for in-rack sprinklers? This is a large warehouse with no sprinkler system. They are using 2x6's for rack spreaders and completely covering them with no flue space. Several issues there... what drives the requirements on the storage practices? Even though the building doesn't require sprinklers, do the code requirements regarding the rack storage apply? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
14 Comments
Glenn Berger
7/13/2023 08:20:22 am
I will start with the easy question first:
Reply
SafetyGuy Bernie
7/17/2023 08:21:40 am
Thank you Glenn for your response. In this case the AHJ is the local fire chief, whom is an outstanding chief in the small town, but is lacking in a full understanding of the code. Also, this building is owned by the local municipal and I think he would be reluctant to inform them of such an expense.
Reply
One could argue that if the storage arrangement or type of storage has changed since the original construction, then the new sprinkler requirements could be enforceable.
Reply
SafetyGuy Bern
7/17/2023 09:12:37 am
Thank you for the response JP.
Reply
Dan Wilder
7/13/2023 08:52:55 am
The original building may not have been required to have sprinkler protection based on the occupancy, storage, storage commodity and configuration, or several other factors at that time. As soon as any of those factors are changed via a required permit submittal (even if a permit was not pulled), i.e. adding a wall, adding an electrical breaker/outlets, adding or removing ceilings...then the city (typically) has the right to reassess any life safety items within the building based on their adopted building and fire codes.
Reply
SafetyGuy Bern
7/17/2023 09:21:22 am
Thank you Dan for the IBC code. You pointed out exactly what I believe about the wood shelving. This warehouse is owned by a municipal electric company. I am their new contracted safety consultant. I have an extensive background in fire protection and life safety code, along with my CFI-1 from 12 years ago, and I was doubting myself on putting it in writing that they must comply with the requirements of NFPA 13 due to the changes. You guys are great. Thank you very much.
Reply
Jon N
7/13/2023 09:45:33 am
It depends on the code being used. If the jurisdiction uses the International Fire Code (IFC), refer to Section 102 (Applicability).
Reply
SafetyGuy Bern
7/17/2023 09:27:26 am
Thank you Jon N, I like how you laid it out in IFC code language. That is my language. You have given me several additional responses in the event they reject my findings from the safety audit. I have become friends with the local fire chief who is the AHJ, and I am confident he will back me as well. Tax payers wont like it much, as it is a municipal building. Great stuff, Thank you.
Reply
Just another AHJ
7/26/2023 11:51:22 am
I agree with Jon, the operational permit alone "should" trigger an inspection under the IFC. During this inspection the fire inspector should note that the high piled storage is not covered adequately by a fire sprinkler system as required. You may be able to argue also that the occupancy classification of the building has changed based on the use and the storage of new types of materials IAW with IBC. An example would be changing a S-2 occupancy type to a S-1 depending on the type of materials being stored. This would be an "change of use" or "change of occupancy" and require the building be brought up to current codes/standards.
Reply
Casey Milhorn
7/13/2023 10:17:29 am
Dan nailed it. Not sure who your represent in all this (contractor, AHJ, owner, engineer, etc.), but depending on your contractual involvement, and even ethical involvement, be careful. You now are aware of changes that may require protection. Make sure you cover your tail, and make the appropriate parties aware.
Reply
SafetyGuy Bern
7/17/2023 09:40:00 am
Thank you Casey, I am a new Safety Coordinator working for Minnesota Municipal Utilities Association, and this is one of my clients which is a municipal power company. With the price of power generation on the extreme rise, they will not be pleased to hear this expense is required. How I look at it; it is much better than having a fire and learning about it afterwards.
Reply
Jesse
7/13/2023 11:40:53 am
This is a complicated question. It all boils down to the AHJ.
Reply
Robert
7/14/2023 10:59:36 pm
Also - the insurance = the underwritten...the policy could deny a claim if a fire occurs and storage of materials differs from the original occupancy/policy.
Reply
SafetyGuy Bern
7/17/2023 09:44:46 am
Great stuff everyone. I thank you for all the information and codes to back them up. I can't believe after 26 years in the safety field I just found your site. I definitely won't forget it. If you ever have an OSHA occupational safety question, I would be glad to assist. Much appreciated.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop June '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
July 2024
PE PREP SERIES |