Can a 4" pump with 4"-6" discharge fitting be used on a private 10" combination line (fire suppression and hydrants)?
NFPA 24 Section 13.1 states that no line less than 6" shall service a hydrant. But does the fact that NFPA 20 Section 4.16 allows the 4"-6" discharge fitting as part of the pump assembly overrule this? Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
4 Comments
Dan Wilder
5/17/2024 07:58:34 am
Two separate standards...cross compliance that is not specifically called out in either standard is not a requirement. Also, based on the question, the 10" feeds the 6" laterals to the hydrants via the combined service piping, the pump sizing would not play into that pipe size requirement, only volume. As a '4" pump' is only available in 300 or 400 GPM volumes, that would be my concern more than the sizing...6" discharge requirements of 750 & 1000 GPM volumes but would already comply with NFPA 24 only because it's a requirement from NFPA 20 (Table 4.28), they are not inclusive or a prerequisite between them.
Reply
Brett
5/17/2024 08:31:50 am
The requirement for a hydrant to be feed with a minimum 6" pipe is to ensure a minimal volume of water availability at the hydrant. When designing any system, but especially one which includes a pump, you really need to thoroughly evaluate the purpose of the system. This will help you determine how much water is going to be needed. The pump can only affect pressure, not volume. However, it must be sized to not reduce the required volume necessary for the system.
Reply
Jesse
5/17/2024 09:16:30 am
I typically refrain from making an affirmative statement about something either way without calcs, but I'm gonna say this probably isn't a good idea.
Reply
Jack G
5/17/2024 09:39:39 am
Residential neighbor hood, H2, commercial?
Reply