For the acceptance testing of a dry pipe sprinkler system, is a 24-hour 40 psi pneumatic test required, or will the 200 psi hydrostatic test alone suffice?
Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments
Anthony
12/5/2023 07:24:43 am
Yes the 24 hr pneumatic test is non optional for dry and pre-action systems.
Reply
Dan Wilder
12/5/2023 07:28:15 am
Nope, you'll need both (References to 2022 NFPA 13). Don't forget the FDC piping as well per 29.2.1.8. Actually, the air test is an alternate to the hydrostatic test in areas as a temp method until the hydrostatic test can be completed.
Reply
Glenn Berger
12/5/2023 08:07:10 am
As others have mentioned, both tests are required for system acceptance.
Reply
Aaron
12/5/2023 09:20:40 am
First hand experience...air will find leaks water doesn't, particularly on threaded joints.
Reply
Jesse
12/5/2023 12:50:17 pm
Yep, both are required. In my area, some AHJs overlook the air test and only want to do the hydro.
Reply
Franck
12/6/2023 01:45:02 am
Confirmed : both required for the reasons mentioned above.
Reply
Sean
12/9/2023 09:00:33 am
they accomplish different things so they cannot be substituted
Reply
sean
12/31/2023 06:56:26 pm
you need both. Also you need both to CYA
Reply