Are hydraulic placards required for NFPA 13D systems?
Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments
Peter Howard
6/13/2023 06:44:54 am
Required? Technically no. It would be in NFPA 13D Chapter 11 if it was in the code, and I'm not seeing it in the 2016 edition.
Reply
Dan Wilder
6/13/2023 08:24:17 am
Considering 13D allows for both a "General Pipe Size Method" (12 step) and a "Prescriptive Pipe Sizing Method" (8 step) in addition to the option of a standard Hydraulic Calculation procedure, other than some basic info for K-factor & max spacing of a sprinkler/max flow rate, getting that deep into the results in unnecessary.
Reply
James Evans
6/13/2023 08:36:26 am
Technically NFPA 13D systems do not require yearly inspections after the initial installation. It seems as though 13D systems are left to the owner to upkeep and call if there is any problems that occur. If the 13D system is installed in a care facility I believe then they are required to have yearly inspections based on the states requirements.
Reply
Jesse
6/13/2023 11:51:23 am
Typically no. We don't include hydraulic placards on our 13D projects
Reply
James Art
6/14/2023 11:27:08 am
Now and then a house is remodelled, added to, so the system needs be updated. I review plans for some AHJ's,
Reply
Alex
6/14/2023 01:46:37 pm
Required - no. But it would be helpful knowing the maximum spacing permitted/design criteria for future renovation projects within the home.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop June '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
July 2024
PE PREP SERIES |