Looking for some guidance on sprinkler layout on eaves and hips. When laying out an attic, if you design with sprinklers directly under the hips, and want to stay below the 8' spacing against the slope, how does the layout work? One direction of the roof would be 4' x 7'-6" max, but the other direction of the roof would be reversed, creating a non-linear coverage area. All of it seems strange to begin with and wondering if I'm overthinking this. We typically don't design with sprinklers directly under the hips, but I'm wondering if we are over designing with too many sprinklers, etc. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
5 Comments
Jesse
10/3/2022 08:18:24 am
Attic layout can be funny. If you are using the Tyco product the data sheet has some excellent examples.
Reply
Eric R
10/3/2022 08:49:12 am
My simple answer is to just use a special application sprinkler! I worked in more attic trusses than I count when I was in the field, and hip roofs were always a challenge. Trying to follow the prescriptive requirements in NFPA 13 can be very difficult when designing in a 3D space like that, and the challenge is compounded when the design hits the field and excess framing elements make it almost impossible to follow the NFPA arrangement rules.
Reply
Alex
10/3/2022 09:00:30 am
Hi,
Reply
Steven
10/3/2022 09:01:13 am
I agree with Eric, I almost always prefer the special application attic sprinklers from a design standpoint. However, they are substantially more expensive and sometimes they won't save you enough sprinklers to justify the cost. When you do have to use standard spray sprinklers, you are certainly right -- sprinkler head layouts at the hips can end up looking a bit strange. I doubt you are overthinking it -- attic layouts can be quite challenging, especially if you are also installing it as a dry system.
Reply
Check out Victaulic’s line of attic sprinklers, which even come in a ‘Low Flow’ scheme which reduces water by roughly 70% resulting in system demand ranging from 130-180 gpm.
Reply