We design fire protection systems for large industrial plants with a large area network running in the kilometers.
In such case there could be chances of surge due do sudden closure of a deluge valve, check valve, or fire pump. We do not have time/expertise to carry on surge analysis on software. I have heard about using tanks for surge. How would we go about sizing an anti-surge tank? Is there any basic guidelines based on fire water flow rate/pump discharge pressure to get first cut sizing of a surge protection tank? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments
Dan Wilder
9/10/2021 07:39:12 am
Reach out to these guys, we've used them on several projects. They have a sheet to fill out and they develop the size of the tank based on the info you provide (Static PSI, operating PSI, size of pipe, viscosity of fluid, size of system downstream of arrestor...)
Reply
Alex
9/10/2021 08:07:46 am
HI Anonymous,
Reply
CJ Bonczyk
9/10/2021 09:38:45 am
I have used on several DOD projects the use of Young Engineering and Amtrol Surge Suppression Tanks. Normally the use will be a vertical style tank and have flanged connections. Some can sit on the floor and be sized and used for the entire manifold and some must be installed downstream of the control valve for each individual system. The bladders will need to be pulled in a vertical position so ensure proper height is allowed for access. Typically the manufacturer can size the tank for you based on the inlet pressure, operating pressure and system demand. Oddly in certain instances of DOD projects they have in the past ignored what the manufacturer recommended and the EOR sized the tank as they saw fit (I do not know why that was the case).
Reply
Mike
9/10/2021 09:44:11 am
We've had mechanical engineers design these but the tanks would have been so large, as may be the case for you, pressure relief valves were used instead.
Reply
Pete D
9/10/2021 11:06:09 am
I agree.
Reply
Colin Lusher
9/10/2021 11:09:14 am
I second Young Engineering. They basically developed the surge analysis and tank sizing used on all NAVFAC and USACOE projects. They'll get your info, and provide suggested tank sizes and locations. That said, their tanks are VERY expensive.
Reply