I am trying to figure out how to protect an existing building that has never had a sprinkler system.
The building peaks at 46'-5" and in that area you can only have a max height of 25'-0 in storage, due to operable cranes in the bay. Additionally, the building is constructed using 12" purlins, so ESFR pendants are out unless we want to put them on return bends. I am trying to give the owner as much storage space as possible, and commodities as they plan to rent the building out to tenants in the future. I have searched through CMSA, CMDA, ESFR and storage to find a situation that best describes it. The issue I always come up on, is the distance from top of storage to ceiling. Every scenario I have looked at, we seem to exceed the 10' or 20' maximum distance. Does anyone have some criteria they used that is close to the situation above? Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments
Peter Howard
2/13/2023 07:54:58 am
A couple of ideas, please take all with a grain of salt:
Reply
Glenn Berger
2/13/2023 08:15:22 am
Storage Occupancies are difficult to provide one size fits all solution. You are pretty much on the right track in your procedures. I did not see any statement on the propose commodity to be stored.
Reply
Todd E Wyatt
2/13/2023 09:05:40 am
The scoping Code (e.g. 2021 IBC) determines “Where Required” an automatic sprinkler system (ASPS) is required per the Occupancy Classifications (OC) of the building.
Reply
Jesse
2/13/2023 09:49:58 am
I'm curious to know commodity to be stored and roof pitch.
Reply
Jay
2/13/2023 10:26:48 am
If the roof pitch is greater than 2/12 then you can't use the high piled storage chapters of NFPA 13.
Reply
Franck
2/13/2023 02:39:51 pm
One solution, if you can find a sprinkler design solution for 35 ft stge in 45 ft bldg, is to consider a 35 ft high storage to design your sprinkler density at 45 ft.
Reply