How would you protect metal shelves that are inside single and double row racks? (photo below) The commodity is Group A plastics, and the ceiling-level is 30-ft and has K17 at 35 psi.
Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
4 Comments
Glenn Berger
5/29/2023 08:09:22 am
I would establish controls on maximum storage heights per shelf. I would also get linear heat detection in the shelving unit to provide some means of early detection. I would also investigate a video smoke detection down each aisle, if possible, as another means of early detection.
Reply
Franck
5/29/2023 11:58:25 am
You can’t
Reply
Jesse
5/30/2023 07:47:01 am
I've seen this before, and had the same questions when doing a risk assessment. How deep are the shelves?
Reply
Peter Howard
5/30/2023 02:36:32 pm
You build a completely solid mezzanine (that extends at least 15'-0" beyond any storage) or ideally an entire floor at the rack level.
Reply