We are bidding a job that may possibly need a 1,250 gpm rated fire pump due to not enough flow from the city. Our test was 43 psi static, 35 psi residual at 872 gpm. We will need to include a ground suction tank.
How do I correctly include or simulate a ground suction tank in my hydraulic calculations? We use the Sigma Hydraulic Calculation program. Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
5 Comments
Alex
7/1/2022 07:31:48 am
Hi,
Reply
Jesse
7/1/2022 08:11:55 am
The fire pump will be you driver for calculation. You can put your water supply node where the tank will be, and set the pump node to the pump ratings: i.e. churn is static, rated capacity is residual / flow and follow the pump curve out with the 150% rating. If your tank has a higher elevation than the pump you can add a couple psi for the water column.
Reply
Steven
7/1/2022 08:33:35 am
Jesse has it right. You won't need to include your hydrant flow test results in the calculation whatsoever. I also haven't used Sigma before, but other calculation packages will let you include a pump curve as the only water supply source. I recommend doing that if the software will let you. If the software does force you to include something for the City supply, then do just what Jesse said, and include the pump flow/pressure curve as your Static / Residual / Flow values.
Reply
Franck
7/1/2022 09:41:23 am
You can take the theoretical curve (commercial curve) provided by the supplier as a first approach.
Reply
7/2/2022 09:12:37 am
I question whether a tank is needed. What size is the
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop June '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
July 2024
PE PREP SERIES |