What is the correct procedure for determining the quantity of the reserve amount of foam, such as FP 3%, for a plant?
I've looked specifically through NFPA 11 and NFPA 16, and can't determine it. Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments
Jonathan Griffin
8/25/2023 08:13:55 am
Look in the 2016 edition of NFPA 11 (printed in 2019) Section 4.3.2.5.2 -- Reserve Supply of Foam Concentrate.
Reply
Pete H
8/25/2023 08:18:15 am
Take with grain of salt, only briefly looked at this:
Reply
Todd E Wyatt
8/25/2023 08:32:17 am
The prior references to NFPA 11 & NFPA 16 are correct but I recommend you verify the editions of these standards based on the scoping Code(s) (e.g. IBC & IFC).
Reply
Dan Wilder
8/25/2023 08:38:48 am
In both 11-21' & 16 - 19' and specific of low-expansion foams for NFPA 11
Reply
Dan Wilder
8/25/2023 08:51:04 am
I put all that in there so that the tank sizing is correct, but hit send prior to the reserve sizing...
Reply
Glenn Berger
8/25/2023 08:48:06 am
I have always just determined my required primary supply and then provided a reserved supply of the same quantity.