We have a Fire Marshal that is asking us to "show how the fill line can refill the [water supply] tank in a maximum of 8-hours, per NFPA 22 Section 14.4.2".
The tank we're proposing will be supplied by an existing well, but we do not have information on well capacity. What parameters should we be looking for on well capacity? Do we have to test for both flow and time? Is the computation on refill as simple as the flow rate (gpm) x time (8-hours) to get the contribution from the well? Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments
Pete H
6/5/2023 06:52:26 am
Do you have the existing well's discharge and flow rate?
Reply
Dan Wilder
6/5/2023 08:02:26 am
Any historical data on the pump available (actual rated head/GPM, how long has it been there, any issues with low flow)?
Reply
Anthony
6/5/2023 08:08:21 am
A domestic well most of the time won't have the fill rate you'll need for your tanks. So that'll be a non-starter in most cases.
Reply
Glenn Berger
6/5/2023 08:09:24 am
There are specialized civil engineers (maybe hydrologists) who can provide this information
Reply
Adam
6/5/2023 08:24:56 am
I've had the same question in the past (not on this forum), and never reached a solid conclusion.
Reply
Pete D.
6/5/2023 01:46:48 pm
Tap into the fill line with a mechanical tee and flow it to obtain a pitot reading.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop June '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
July 2024
PE PREP SERIES |