When you have a common office building that is classified as a Light Hazard but you have some rooms that may be Ordinary Hazard such as storage rooms and others.
When you have your layout and one or more of these rooms ends up in your design area, how do you proceed in the calculation? 1.- Do you calculate 0.10 gpm/sqft over 1,500 sqft? 2.- Do you calculate according to Chapter 23 Sections 23.4.4.2.4 and 23.4.4.2.5 specifically for that room even if it is one or two sprinklers? 3.- Do you calculate everything with the density and area for the hazard of that room even though everything else is Light Hazard? 4.- Do you calculate 0.10 gpm/sqft over 1,500 sqft and ensure that the sprinklers inside the room discharge at the minimum density for the hazard they have? This may be very general and definitely every project is different but every time I run into this I have this same question. I was told to just calculate everything as a Light Hazard but my curiosity always keeps me thinking about it. Moderator Note: This question is different, but similar to: www.meyerfire.com/daily/ordinary-hazard-within-light-hazard-building Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
4 Comments
Matt
5/3/2021 08:08:01 am
If a sprinkler in your design area falls within an OH room or space, simply calculate those affected sprinklers at the revised density (0.20 gpm/sqft).
Reply
James
5/3/2021 08:28:21 am
Right, I'm with Matt. Option #4 with a caveat:
Reply
Franck
5/3/2021 08:42:03 am
Much as been said at: www.meyerfire.com/daily/ordinary-hazard-within-light-hazard-building
Reply
Dan Wilder
5/3/2021 10:54:27 am
Big reason why there needs to be a push for a distinction between "Hydraulically Remote Design Area" vs. "Remote Area". I'm with the #4 option as well and Franck sums it up well.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop June '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
July 2024
PE PREP SERIES |