I'd appreciate some advice.
What's the best way to regulate pressures on a combined sprinkler (OH2) and Class 3 standpipe system? Obviously the pressures required vary between sprinklers, 2-1/2" standpipe outlets and 1-1/2" hose rack connections. Pressure regulating valves are expensive to put in on all connections, but I was thinking about using pressure regulating valves for the 2-1/2" standpipe outlets. I think it's great that we can all share our combined experience on this great website - thanks in advance! Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments
Alex
6/12/2023 06:40:57 am
First, I would verify which system has the higher pressure demand. Then, I would provide PRVs on the respective system.
Reply
Pete H
6/12/2023 06:50:35 am
Pressure regulating valves anywhere your system is going to exceed 175 psi (and therefore exceed the listed pressure of many sprinkler fittings).
Reply
JI
6/12/2023 08:29:44 am
-When standpipe pressures (city water, building fire pump, etc.) are over 100 psi and under 175 psi, standard 2.5" hose valve, pressure restricting (valve reduced under flow conditions only) type 1.5" hose valve. 2" test riser with test ports for 1.5" valve.
Reply
Casey Milhorn
6/12/2023 08:56:54 am
Without more detail, your answer will vary. Also, there are several approaches to pressure control that all could work and could meet code, some might just be more economical and/or practical than others. Mostly the solution is going to be based on the height of the building and local/state AHJ requirements. Remember that it's the firefighters that will be going in and using these hose valves when it hits the fan, with their lives in danger. I fight very hard to give them what they want, and I put their opinion above everyone else's.
Reply
Glenn Berger
6/12/2023 09:05:57 am
Please indicate the supply side maximum pressure that you want to regulate. Initially my concern would be for the 1-1/2 inch hose having excessive pressures for "untrained" people.
Reply
Dan Wilder
6/12/2023 09:07:34 am
Sprinkler and standard 2½" hose valves in a Class I or III system have a min 100PSI (HV only) & max 175 PSI (both). The 1½" hose valves/stations have a min 65 PSI and max 100 PSI.
Reply
Thanks to all for these really useful comments. I will be allowing a 4" combined galv drain line. I was hoping that the fire truck pump wouldn't go over 150psi, but I guess it could? As Casey says, we need to make sure that the fire department get what they want and we will be in consultation with them shortly. We have asked for a dispensation to go from a class 3 to a class 1 standpipe system, because I too am worried about untrained personnel using fire hoses - the FD will advise on that I'm hoping. A pressure mapping excercise is a great idea and I'm certainly taking that on board. Thanks again!
Reply