How do I, as an AHJ, address contractor scope limitations?
Project where an installer presents plans to replace 328 sprinklers and is changing some pipes out. Many times the installer says they're only responsible for pipe from the riser - not for a hydrant flow tests. What is the best way to navigate this to be sure that there's still sufficient water available? It could be a one-for-one replacement, but what if there's significant work being done - what code basis is there to make sure than an effectively-new system can work with today's water supply? Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
9 Comments
Pete H
8/10/2023 07:30:04 am
While their contract may only be responsible for pipe to riser, they still would have to calculate a sufficient modification to a system (as in: not a 1:1 relocate or a reduction in hazard or demand.)
Reply
Alex
8/10/2023 07:33:09 am
When you replace or relocate sprinklers, you must provide hydraulic calculations to demonstrate adequate flow and pressure. To conduct these calculations, water data is essential. Moreover, if you are fed directly from the municipal supply, you need water data from within the past year.
Reply
Jesse
8/10/2023 08:11:09 am
This is a really good question, and should be a good discussion.
Reply
Daniel LeFave
8/10/2023 08:17:58 am
As a contractor, we always specify in our scope of work that we start at a flange above floor and furthermore specify what we intend to provide for our services. This does not limit us to new hydraulic calculations and often we perform a new hydrant flow test or water data has been provided to us along with the new/updated design criteria by the engineer of record. For example, we recently had a warehouse job and the GC limited us to the office scope only as there was an existing system in the warehouse, but the occupancy was changing. The AHJ requested that calculations be performed in the warehouse to the new system demand requirement and after a bunch of back and forth it was decided this was a requirement for TCO and we were contracted to calc the system. It seems that most GC's and owners only care about drywall going up until TCO time comes around and then they remember about the life safety systems.
Reply
Dan Wilder
8/10/2023 08:54:20 am
First, what provisions are adopted within the IFC, specifically Section 105.6 for required permits? Then, referencing 106.2.2 for the requirements of Shop Drawings per Chapter 9.
Reply
Glenn Berger
8/10/2023 09:09:06 am
To your original question - Does your jurisdiction is construction permits and certificate of occupancies?
Reply
SCHULMAN
8/10/2023 09:22:24 am
Lots of good info in the responses already.
Reply
Eric R
8/10/2023 11:43:26 am
To add to the discussion, what happens (or should happen) when the contractor does get a new flow test, performs hydraulic calculations for the scope of their work (which can be easily modified if need be within the scope of work), applies for a permit showing their work has the required water supply, but the flow test shows that the water supply has degraded below what was required for the original system design per the hydraulic placard?
Reply
Pete H
8/10/2023 02:03:51 pm
IMO (so take with grain of salt):
Reply
Leave a Reply. |