We're doing a full remodel on an existing, vacant, 3-story building.
During the remodel, there won't be any heat in the building. There is an existing fire sprinkler system that would freeze during the winter. How should we proceed during the remodel? Are we required to keep the sprinkler system active? Is the owner required to provide heat? What would you recommend from experience? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
5 Comments
Alex
10/7/2021 06:39:48 am
Hi Anonymous,
Reply
Franck
10/7/2021 08:09:38 am
Insurance point of view (from Europe - so mostly common sense based and not US National code based)
Reply
10/7/2021 08:57:38 am
It is clear in the codes that it is the owners responsibility to maintain a heated environment above 40F and if they cannot they must shut the system down and provide a fir watch. This is addresses in several areas of the code:
Reply
Jesse
10/7/2021 10:18:05 am
I'm presuming that there won't be any tenant spaces occupied as there won't be any heat?
Reply
sean
10/8/2021 08:51:22 am
Fire code requires you to maintain system as installed and required for buildings during construction. Heat will have to be provided.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop June '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
July 2024
PE PREP SERIES |