How much engine oil can be stored in a building with an Ordinary Hazard Group 2 (OH2) sprinkler system?
We're working on a repair garage and NFPA 13 (2019) classifies repair garages as OH2 in the appendix. It seems reasonable that some amount of engine oil would be allowed to be stored. However, the NFPA 13 definition of OH2 doesn't allow for flammable/combustible liquids, but EH1 and EH2 allows for some unspecified amount of flammable/combustible liquids. NFPA 13 section 26.2.1 states that sprinkler system discharge criteria for the protection of flammable and combustible liquids shall comply with NFPA 30. NFPA 30 (2021) table 10.7.1 allows for unlimited IIIB liquids to be stored in mercantile occupancies with an OH2 sprinkler system. Can this mercantile section be applied to a storage occupancy? Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
5 Comments
Pete H
10/13/2023 06:51:30 am
If you're in storage, you're governed by NFPA 30 Chapter 16, not Chapter 10, as you're no longer a mercantile occupancy.
Reply
Dan Wilder
10/13/2023 09:14:10 am
By definition - No, these are definable and separate areas.
Reply
Anthony
10/13/2023 09:58:25 am
I 100% agree with Pete and Dan here. You can't apply mercantile code to storage applications. There are a bunch of assumptions made by the code based on the occupancy of an area.
Reply
Casey Milhorn
10/13/2023 11:38:24 am
I also agree with Dan and Pete's assessment and are a lot better than me at the code side. From a more practical fire sprinkler contractor/designer perspective, remember that NFPA 13 classification is only part of it, and in this case flammable/combustible storage cabinets might be part of the overall solution along with other possibilities. I know as a sprinkler designer, sometimes I have blinders on and I think we need to be the problem solver for everything by just upping the hazard. It's good to remember we are just part of the overall fire protection scheme and that it's important that a competent FPE or PE be involved.
Reply
Glenn Berger
10/13/2023 12:26:44 pm
Take a look at the specific flash point(s) of the engine oil that may be used at this location. Some motor oils have a very high flash point and might be able to be classified as a Class IIIB combustible liquid.
Reply