NFPA 20 dictates the number and size of hose valves according to the pump rating, but is there any specific requirement on how many are to be used during testing?
How is that determined? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments
Anthony
10/6/2023 07:59:43 am
Should use one 2 1/2'' hose per 250 gpm.
Reply
Jesse
10/6/2023 08:07:43 am
All of them.
Reply
PEter
10/6/2023 08:14:21 am
Not quite. NFPA 20, 2016 Table 4.27A specifies the number of hose valves. It is a common misconception that it for every 250 GPM of the pump a hose valve is provided. For example: 1,250 GPM, 1,500 GPM and 2,000GPM all require 6 hose valves.
Reply
Glenn Berger
10/6/2023 08:17:43 am
The above answers are correct. But here is a slightly different answer - As you work your way through the required flow rates during the test procedure then more hoses / hose valves are required.
Reply
Mike
10/6/2023 08:51:27 am
As Peter mentioned above there is no explicit requirement. If you're using long hoses you'll want more valves to keep friction loss in the hoses in check etc. We actually had a client fire pump tested 1 year out and fail only to end up looking rather bad because our "big" test trailer with 6 outlets was in use elsewhere so they only used 3 outlets to test a 1500 gpm pump and it was creating excessive restriction. After some back and forth our tester went back out and tested with 6 hoses and lo and behold the pump worked fine. We had some other issues on that job but between those and the bad test I think we lost that customer which is disappointing to say the least.
Reply
Dan Wilder
10/6/2023 09:06:38 am
Interesting...maybe someone from NFPA 20 can chime in
Reply
Franck
10/6/2023 10:14:59 am
You need enough to test the pump up to 150% of its nominal flow at least once per year.
Reply
CONNOR R
10/6/2023 10:33:16 am
It depends on the hoses and equipment that you bring. Each test device e.g. hose monster is calibrated to be used in a certain configuration, and with a certain length of hose. As long as you are using the equipment consistently and in accordance with the manufacturer's listed instructions, you are fine.
Reply