Where does NFPA 20's jurisdiction end?
Is it possible to have pressure reducing valves in a suppression system, downstream of a fire pump? NFPA 20 seems to not allow for that, but does NFPA 20 apply downstream? If so, how far? In the standard it says up to a last control valve or something like that - what control valve(s) is it referring to? Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments
Dan Wilder
11/1/2023 08:10:08 am
NFPA 20 (22' Ed referenced) discusses the "discharge valve" or "discharge isolation valve", more specifically in 4.17.8 "A listed indicating gate or butterfly valve shall be installed on the fire protection system side of the pump discharge check valve". The handbook also states in 4.17.11:
Reply
James Evans
11/1/2023 08:23:07 am
Another good question is "How far upstream from the pump does NFPA 20 cover?" Since pressure regulating valves are not allowed upstream of a fire pump. In some cases a pressure regulating valve would be beneficial upstream of a fire pump as opposed to downstream.
Reply
Dan Wilder
11/1/2023 10:44:28 am
4.16.1 - 4.16.1.1
Glenn Berger
11/1/2023 08:30:46 am
Totally agree with Dan.
Reply
Anthony
11/1/2023 08:46:28 am
NFPA 20 explicitly says you can use a PRV downstream of the pump where required.
Reply
Dusko Nikolic
11/2/2023 04:09:08 am
Thanks for the help. Much appreciated
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop June '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
July 2024
PE PREP SERIES |