I wanted to pose the question on hazardous material storage lockers. We wish to protect the locker in accordance with Chapter 14 of NFPA 30 and have rated it for 4-hours to eliminate the need for fire separation distance to the immediately-adjacent main building as allowed.
The locker will not be structurally attached and will only have flashing connecting the two to keep out the elements, garbage, and animals. The locker will only have people in as necessary to get the liquids out. The main building has a door on the "exterior wall" that opens and "reveals" the 3-hour rated hazardous material locker door, which you have to open to get inside the locker. NFPA 30 2015 handbook Section 14.4.3 denotes that lockers over 1500 sqft should be protected permanent building such as attached buildings or warehouses. Our locker is under the 1500 sqft requirements so therefore I would say we are not a building but a "locker". Therefore, the exterior wall openings allowances of IBC (2015) Table 705.8 would be to the lot line (over 10ft) and not the locker itself (0ft), allowing our client to access the locker from the inside of the main building and not having to go outside to access it from the exterior. I was wondering if anyone has had a similar experience or if we should just call it part of the main building and protect it as such and lose the allowances of Chapter 14. Thanks in advance! Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
4 Comments
Jesse
3/2/2022 08:10:31 am
This really is a question for the AHJ as they will have overall say in the matter.
Reply
Alex
3/2/2022 08:52:36 am
HI,
Reply
Todd Wyatt
3/2/2022 11:59:02 am
Be careful using the term "Fire Wall" as this has specific prescriptive requirements per 2021 IBC Section 706 Fire Walls (see https://codes.iccsafe.org/content/IBC2021P1/chapter-7-fire-and-smoke-protection-features#IBC2021P1_Ch07_Sec706).
Reply
Eric D.
3/2/2022 09:04:15 am
Well, the first issue is separation. Remember, the Code defines Fire Separation Distance as the distance measured from the face of a building to the closest interior lot line, centerline of a street or public way, or the distance to an imaginary line between two buildings on the same lot - this last section is critical in this example)? Is the building far enough away from the main structure or are openings and walls protected from each other in accordance with the adopted codes (which I believe you said was not the case between the building and the locker)? If the separation is not there - boom, it is now part of the main building and needs to be protected as such. If fire separation is provided (via walls, glazing, opening protection, etc), then you can consider the "locker" as a separate building and may be able to get an AHJ to see it that way and not have protection.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop June '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
July 2024
PE PREP SERIES |