We're working on an aircraft hanger with a foam system. I can't quite nail this down, as NFPA 409 and the UFC don't spell this out - do the hangar doors need to be open, or closed, in case of a fire or to test the foam system?
Again, don't see any guidance spelled out in either standard. Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
19 Comments
Alex
2/28/2022 08:01:10 am
Hi,
Reply
Dave
2/28/2022 03:24:28 pm
What about the hangar door question?
Reply
Jack G
2/28/2022 08:11:39 am
I have a pic of an operating deluge system in a helicopter aircraft hanger. Wish I could attach it.
Reply
Moderator
2/28/2022 08:12:33 am
Send it to us at [email protected] and we could probably get it hosted.
Reply
Derek
2/28/2022 08:22:39 am
2022 NFPA 409 only states that a functional test of the doors needs to be done annually with no flow. In addition, 8.2. allows for open doors for multiple types of systems. I guess it's AHJ interpretation?
Reply
Heather Barreto
2/28/2022 01:02:40 pm
I will check this! Thanks
Reply
Dan Wilder
2/28/2022 08:28:57 am
I've never had this requirement come up (not saying it isn't a requirement somewhere but the commercial & military hangars I've done have not required it). We actually test with the doors partially open anyway (mostly for containment so the foam doesn't roll out onto a runway) and for the looky-loos who are there to witness..
Reply
Heather Barreto
2/28/2022 01:05:01 pm
Thanks!.. Well I guess I need to check with AHJ about what they want
Reply
Glenn Berger
2/28/2022 08:42:08 am
I have required the doors to be closed to ensure that the depth of the foam is obtained.
Reply
Brad K
2/28/2022 08:53:47 am
First, I recommend closing the doors for the test. You DO NOT want air pressure or wind to take test foam out and create potential for concern near an active air strip. Not to mention EPA issues.
Reply
Heather Barreto
2/28/2022 01:08:26 pm
Awesome Comment. Thanks for your advice.
Ryan G
2/28/2022 08:45:22 am
The idea of a foam system is to smother the fire. I order to accomplish this, you need to contain the foam. To contain the foam, the hanger door needs to be shut. To work effectively, the door should be closed prior to the system discharging.
Reply
Heather Barreto
2/28/2022 01:09:05 pm
Thank you for your comment! very hepful
Reply
Jesse
2/28/2022 08:59:26 am
Its AHJ interpretation usually.
Reply
Zackery Geddies
2/28/2022 09:50:32 am
Take a look at NFPA 11 the Standard for Low, Medium and High Expansion Foam section 7.7 Operation and Control of Systems and 7.12.4.1.1.2. Doors are required to close automatically before or simultaneously with the start of the foam discharge.
Reply
Heather Barreto
2/28/2022 01:09:42 pm
I will check this ! Thank you for your comment.
Reply
David Toshio Williams
2/28/2022 02:46:17 pm
A "little" sidebar... we have a job under construction at an Air Guard Base and we got direction from the Government that work on the HE foam was to stop and the job would be changed to a conventional (preaction in this case) sprinkler system only. Apparently the loss of planes is less of an issue versus the risk/liability of the AFFF and HE systems. Sounded like a change nationally.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop June '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
July 2024
PE PREP SERIES |