Would the rack storage of non-encapsulated, Group A, unexpanded plastic commodities, stored in solid plastic containers (totes), be considered cartoned or exposed?
NFPA-13 Section 3.9.1.1 defines cartoned as storage consisting of corrugated cardboard or paperboared containers fully enclosing the commodity. NFPA-13 Section 3.9.1.13 defines Exposed Group A Plastic Commodites as those plastics not in packaging or coverings that absorb water. This leads me to think that any rack storage of Group A unexpanded plastics within solid plastic containers should be considered exposed, as these are not cardboard or paperboard nor does plastic absorb water. Thanks in advance! Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments
Anthony
4/5/2023 08:02:03 am
Definitely not cartoned as the packing material cannot absorb water.
Reply
Jesse
4/5/2023 08:06:21 am
Group A unexpanded, Exposed, not cartoned.
Reply
Alex
4/5/2023 08:11:45 am
Since the non-encapsulated, Group A, unexpanded plastic commodities are stored in solid plastic containers (totes) rather than corrugated cardboard or paperboard containers, they do not meet the definition of cartoned storage according to NFPA-13 Section 3.9.1.1.
Reply
Glenn Berger
4/5/2023 08:18:43 am
Exposed would be correct. The language stating commodity needs to be defined as the entire unit being stored.
Reply
NK
4/5/2023 08:22:25 am
Make sure the plastic totes are not considered open-top containers in which case they are outside of the scope of NFPA 13.
Reply
Todd E Wyatt
4/5/2023 08:40:49 am
I recommend review of the adopted Fire Code (e.g. 2021 IFC) for the identification and classification of COMMODITIES.
Reply
Todd E Wyatt
4/5/2023 08:42:58 am
REFERENCES
Reply
Franck
4/5/2023 11:04:27 am
Note that even if inside the totes there is no exposed unexpanded group A plastic, you may consider it as exposed unexpanded group A plastic as the fire will affect mostly the totes regarding its behaviour (quick surface spreading on non water absorbing surface), unless you have a commodity inside that could limit that effect (such as water in plastic bottles that is not expised group A plastic despite the plastic outside).
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop June '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
July 2024
PE PREP SERIES |