We have a project design for a single room (26'-0" x 14'-6", height of 13'-2"). The room is noncombustible and is solely for the storage of one large metal diesel fuel storage tank in the basement of a hospital. The tank is under 8-ft tall. I have researched NFPA 13, 16, and NFPA 30. I used the tables for sprinkler type and criteria.
My confusion is the amount of storage and the size of the tank. The tables in NFPA 30, starting with Chapter 16.5.2.1, have guidelines for tank sizes up to 60 gallons only. This is a much larger, metal, stationary tank (3,000 gallons). What table or design criteria can be used? K-factors of 8.0 or 11.2 - and 0.30 or 0.40 density? We will be using foam for this project and I just want to be sure that I'm approaching and educating myself for the correct approach without missing or violating limitations within NFPA 30 (or the other standards). Thanks for the help! Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments
Jose Pinies
11/8/2023 08:38:15 am
I´d like to know too
Reply
Adam
11/8/2023 08:48:11 am
I am not experienced in this topic, either, but it appears that NFPA 30, Chapter 16 does not apply due to such tanks being excluded under 9.1.4 sentence (2).
Reply
Anthony
11/8/2023 09:34:30 am
What we're missing is a code path something pointing you to a particular code/standard. Generally building code will point you to NFPA 13. 13 will point you to 30 and 30 will point you to 11, 15
Reply
Eric R
11/8/2023 10:44:16 am
If the jurisdiction has adopted the ICC standards then tank storage of flammable liquids actually is covered via the IFC under chapter 57.
Reply
Anthony
11/9/2023 01:33:40 pm
Good to know! Thanks!!
Jesse
11/8/2023 10:07:37 am
I'd like to know more about the tank and the room. Regardless, 13 will push you toward NFPA 11
Reply
Michael P Venneri
11/9/2023 07:13:55 am
It is not immediately obvious but as stated above, some applications are contained in the IFC for protection of flammable liquids. These designs are acceptable to most unless the IFC is not adopted by the Jurisdiction.
Reply
Franck
11/11/2023 04:21:35 am
There is no detailed/precise information in NFPA 11 for the design parameters of the sprinkler/deluge system (chapter 6).
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop June '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
July 2024
PE PREP SERIES |