Under the "Protection of piping against damage where subject to earthquakes" NFPA 13 requires "listed flexible pipe couplings" to be installed where pipe passes over seismic joints or building expansion joints.
Is there any similar requirement when the building is not subject to earthquakes? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments
Pete H
4/7/2022 06:40:24 am
Not seeing anything in NFPA 13 (2016) outside of Section 9.3, which is protection of piping against damage where subject to earthquakes.
Reply
Glenn Berger
4/7/2022 08:05:52 am
Flex couplings are required at seismic expansion joints. Flex couplings can be used in all locations.
Reply
Franck
4/7/2022 09:13:33 am
I have seen such practice, when buildings were possibly subject to settlement (soft soil).
Reply
Alex
4/7/2022 11:39:54 am
Hi,
Reply
Jack G
4/7/2022 10:21:12 am
Nfpa allows less space around pipes where they cross thru floors, fire walls, masonry walls, where the couplings on either side within a certain distance are flexible couplings.
Reply
Dave
4/7/2022 10:59:04 am
I see, you are pointing out that since 9.3 states “Where Subject to Earthquakes” (Moved into its own Chapter 18 in the 2019 edition) that the subsection on flexible couplings only applies in areas subject to earthquakes. (Because it is always important to understand the hierarchy of the numbering). I have never designed in areas NOT subject to earthquakes so I have never considered that. (Conversely, I have reviewed plans from freelance designers in non-seismic zones who are not familiar with the requirements nor efficient bracing design). In the handbook edited by Matt Klaus, he states “the AHJ and the system designers should come to an agreement early on in the project to determine whether or not protection against seismic damage…will be required. The determination is typically driven by the building code and hinges on the location of the project and the nature of the occupancy of the building.” The handbook states NFPA 13 does not address the issue of where earthquake protection is to be provided, however SEI/ASCE 7 is adopted by reference in current model building codes. Interesting question.
Reply
Dave
6/15/2022 02:25:59 pm
Actually, my last statement that the clearance allowance does not apply to floor penetrations is refuted by the way NFPA #13 refers back to the floor flex coup requirement. For example, in the 2016 edition, 9.3.4.5 refers back to 9.3.2.3.1(2)
Reply
Max
4/7/2022 05:18:54 pm
Flex coupling could be used to follow the slope of the roof in some cases.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop June '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
July 2024
PE PREP SERIES |