We are completing the build of a 95,000 sqft, 2-story facility. The sprinkler installers are using two manufacturers of fittings and couplings.
Our construction specifications require the fittings, couplings, and gaskets to be from the same manufacturer. They have installed fittings (elbows, tees, etc) from one manufacturer with couplings from another, and vice versa, in multiple areas. I am concerned that any issue later on with that condition could be problematic with liability. I understand there are specifications and tolerances the manufacturers must meet - but is this an issue? I am the AHJ as well as the owner (this is a state building). Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
20 Comments
Alex
10/29/2021 06:59:20 am
Hi Anonymous,
Reply
Dan
10/29/2021 08:08:21 am
Victaulic and Anvil. I have since learned that these are basically Viking.
Reply
Alex
10/29/2021 08:36:14 am
Hi Dan,
Greg
11/2/2021 04:00:37 pm
As far as I am aware Victaulic strongly discourages, if not possibly does not allow this
Glenn Berger
10/29/2021 08:07:22 am
Should not be a problem as long as both products are listed by a nationally recognize testing lab.
Reply
Michael
10/29/2021 08:09:34 am
Typically, it is only a real issue when it pertains to CPVC. Due to some of the solvents that one manufacture may use to adhere piping may not be compatible with the other. As long as they are FM (approved) or UL (Listed) I wouldn’t think it would be a very large deal with steel or iron materials. They should all go through a similar listing and testing process. However, If you know the manufactures of the fittings and couplings you could reach out to the respective companies and see if they have an field incidents where other manufactures were non-compatible for any reason.
Reply
RJ
10/29/2021 08:11:15 am
What you have said in your question answers it for you. 'Our construction specifications require the fittings, couplings, and gaskets to be from the same manufacturer.' If you are not going to have the installers follow the specifications, why have specifications?
Reply
martin moffitt
10/29/2021 01:33:55 pm
Totally agree and why did it take this long to relize the cotractor was not adhering to the specifications in the contract?? not looking to beat anybody up
Reply
HJ
10/29/2021 08:37:15 am
Construction specifications are given for a reason. Your contractor would have based their project bid on those specifications, and agreed to follow them by signing the contract. As the AHJ, you may have the authority to amend your agency's construction specifications, if necessary.
Reply
Jack G
10/29/2021 08:43:00 am
Mechanically they should work as they are built to the same spec.
Reply
Jesse
10/29/2021 08:45:26 am
Usually it isn't an issue. A lot of branded products are manufactured by third parties and labeled differently.
Reply
Kellery
10/29/2021 09:11:37 am
While as long as they are using apples to apples, it should be a problem as others have stated they would be manufactured to the same spec.
Reply
Todd Wyatt
10/29/2021 09:11:49 am
This is a contractural issue for the Owner (e.g. the State) to determine if this "noncompliant" Work is acceptable. The Contractor is required to provide the Owner with the Project per the Contract Documents (Drawings and Specifications). Most Specifications provide the Contractor instructions to request a substitution during the submittal process. If the Contractor skipped this step, submittal the "noncompliant" products, and they were reviewed and accepted, the Owner still has authority (depending on the Specifications submittal language) to require the Contractor to provide fittings from a sole source. The Owner can also accept the "noncompliant" Work as is. I would recommend reviewing the warranty information as it may be voided if all fittings are not from a sole source.
Reply
CJ Bonczyk
10/29/2021 09:12:03 am
You should have the contractor provide you with the technical data on both the coupling being used and the fittings. You can request that the contractor provide a letter from the manufacturer for both products that there is no installation warranty and or compatibility issues of the items being mixed during installation. If both manufacturers state that there is no issue you are fine. If they bring up anything regarding warranty/compatibility/integrity then you can easily argue your case. Additionally the contractor signed a contract and provided a scope. Review those items as they are bound to what they agreed to and if they chose not to follow it you have every right to make them adhere to the requirements as outlined in the execution specifications.
Reply
10/29/2021 09:26:22 am
For Installation of Victaulic End Caps with Victaulic Installation-Ready Couplings:
Reply
Chad
10/29/2021 09:46:16 am
From one AHJ to another… unless you want to enforce the contract specs (assuming the brand was spec) it’s not a code issue… unless improperly installed as other alluded to.
Reply
Dan
10/29/2021 09:59:19 am
We did have a meeting with the Architect, Contractor, Engineering firm, and sprinkler installer. The specs came from the architect/engineers and became a concern for me when I saw what was being installed versus what was submitted. The warranty is one year from substantial completion no mater what was used.
Reply
David Kendrick
10/29/2021 10:39:53 am
This is restating information from your original question statement.
Reply
JackG
10/29/2021 02:01:20 pm
If I correctly remember, Vic coups and fittings , you do not have to torque the bolts on the couplings. Anvil couplings, and anyone else’s, you do.
Reply
Eric
11/3/2021 11:35:41 am
As a side issue to this concern, be aware that grooved fittings from different MFGs in particular having different equivalent lengths for hydraulic calculations. Newer design programs utilizing BIM processes allow the designer to pick a specific MFG when placing fittings in the sprinkler piping model. The fittings are then included in parts lists for ordering and included in the hydraulic calculations.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop June '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
July 2024
PE PREP SERIES |